    Confused Mismatched air handler
    Trane 3.5 ton condenser
    Trane 3.0 air handler
    2000 sq ft home-10 yrs old
    Air handler coils ice and drip from filter area.
    Energy bills have gotten outrageous-approaching $500
    Service man cannot balance system.
    Would a matching air handler improve efficiency enough to offset replacement or should I replace entire unit?
    Aug 2008
    You are trying to cool 2000 sq. foot home with a 31/2 ton unit no wonder your elect bill is so high I have a 5 ton on my 2000sq ft. home When the temp hits 100 it has arough time just keeping the home at 78 I would look into may be going a little bit bigger on the tonnage.
    NW AR
    3.5 will cool 2000 in some instances. The main issue is the 3 ton a/h matched to a 3.5 ton cond. He will never get it to balance. It should have never been installed like that. Did you get a used one cheap or something???
    You should have a 4ton a/h and yes it would absolutely improve efficiency.
    Jul 2001
    Gold Coast of Connecticut
    Like a bigger unit will save energy..........hmmmm.!
    You should look into installing a matched system in your home of the correct size to properly cool your home.
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
    NW AR
    Even a mismatched 3.5 with a 4 ton coil would beat what hes got.
    Oct 2008
    The system was in the house when I bought it. I know a guy who will can install a 3.5 ton air handler for a reasonable price. Should I look at the 4 ton?
    You said teh bills have gotten out of hand, were they reasonable at one time.
    What area do you live in.
    Is it a high humidity area.
    Naples, Fl
    1. 3.5 tons on 2000 ft is not out of line,
    2. The system maybe correct (matched); Trane engineers systems like this; providing that both units are made by Trane.
    3. As Been noted; has something changed?
    4. Arbitrarily doing anything is just that.
    Oct 2008
    Was dripping pretty bad. Serviceman overcharged system to stop drip. Next power bill was high. He took some freon out and bill came back down some,but started dripping every now and then. System just won't balance. Live in deep south with high humidity. Worried because winter bills are usually a good bit higher. By the way, swimming pool accounts for about 75-100 of the 500 dollar power bill. Just wondering if changing the air handler so that the system will balance will get my efficiency where it needs to be. Thanks!
    Ok.
    It may have been installed like this to remove more humidity.
    On systems like this, you need to still keep the air flow up closer to what the outdoor units nominal rating is.
    Good chance it needs a good cleaning.
    You need a tech that can check performance.
    Not just grab the suction like and add gas until its cold. Or just adds gas until teh vapor pressure is above freezing.
    When you do have it replaced. Consider a VS blower. It will aid in moisture removal. And you can have a system where teh indoor and outdoor units are a closer match in size rating.