Thread: LON .XIF file

  1. #1
    Join Date
    Feb 2008
    Posts
    225
    Post Likes

    LON .XIF file

    Performing a Lon job with a Mitsubishi split system going back to a NAE.
    I do not have an .xif resource file.
    How can I upload the .xif file to put in the NAE as a resource file?

  2. #2
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    What is your network management tool?

    I am familiar with Lon and Lonmaker, but not with the NAE.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  3. #3
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    I have the latest Lonmaker

  4. #4
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    Drop a generic Lon device on the drawing from your lonmaker basic shapes stencil. Choose your interface type - FT-10/whatever it is and make sure you have a channel of that type on your drawing. Name it and then choose upload from device on the .xif file. I've always then service pinned the device to get the NID. Anyway once it's done commissioning you can then drop a function block referencing your new device and make connections.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  5. #5
    Join Date
    May 2005
    Location
    North America
    Posts
    78
    Post Likes

    Nodeutil

    The LNS tool can commission without a xif, but the NAE requires one. The easiest is to use Nodeutil to connect to the device and generate a xif file. Then just add the xif to the NAE as a resource.

    Nodeutil182 I believe is the latest, available free from echelon's web site.

    poochz
    There is a way that seems good to man, but in the end leads to death.

  6. #6
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    I will try and let you know....

    Thanks!!!

  7. #7
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    Started to do your suggestion but then I received
    the Mitsubishi CD with the .XIF file on it.
    Loaded the standard and the device.xif files in NAE35 Lon
    as resource files.
    Rebooted NAE.
    It found the device but when I try to discover
    points, the NAE locks up then reboots.
    NAE version is 4.0
    Any suggestions???

  8. #8
    Join Date
    Apr 2007
    Location
    Seattle
    Posts
    47
    Post Likes
    Did you build a LON network? You should be able to see both devices online thru your LON interface.

  9. #9
    Join Date
    Mar 2006
    Posts
    3,639
    Post Likes
    Quote Originally Posted by mechinc View Post
    Started to do your suggestion but then I received
    the Mitsubishi CD with the .XIF file on it.
    Loaded the standard and the device.xif files in NAE35 Lon
    as resource files.
    Rebooted NAE.
    It found the device but when I try to discover
    points, the NAE locks up then reboots.
    NAE version is 4.0
    Any suggestions???
    That sounds like par.

  10. #10
    Join Date
    Mar 2007
    Location
    New Castle, DE
    Posts
    99
    Post Likes
    See: http://cgproducts.johnsoncontrols.co...t.aspx?CID=34#

    In addition, the LONWORKS network integration requires two standard resource
    files named STANDARD.TYP and STANDARD.FPT. The final required resource
    file is the default NV Configuration Data file. This required resource file, in a
    default state, is automatically added to the NAE resource file list when adding the
    LON Integration object. This default file must be updated with the actual installed
    configuration data by sending the LONWORKS network image to the NAE from
    MCL Tool

  11. #11
    Join Date
    Mar 2007
    Location
    New Castle, DE
    Posts
    99
    Post Likes
    You need to also set the NAE and devices on the same domain!! Do this with a lon managment tool.

  12. #12
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    Quote Originally Posted by CascadeControl View Post
    Did you build a LON network? You should be able to see both devices online thru your LON interface.

    Yes, the lon network is built and I can see points in the field from Lonmaker.

    I cannot discover the points in the NAE.

  13. #13
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    Quote Originally Posted by OutOfControlMan View Post
    You need to also set the NAE and devices on the same domain!! Do this with a lon managment tool.
    I will check tomorrow!!!

  14. #14
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    The domains are the same however here is the other info
    under the device Hardware tab.

    Manufacturer: Mitsubishi Electric Corp.
    Device Class: SPIDDataFile Error
    Device SubClass: Network Management
    Transceiver: TP/XF-1250
    DSN1: 37/01/01
    XIF Present: False

    Why error by Device Class?
    Is the transceiver correct?
    Any suggestions?

  15. #15
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,281
    Post Likes
    It does look like the transceiver is the problem. My guess is that the NAE is FTTP-10. The baud rate is much higher on the TP/XF-1250. That is generally used for backbones or high speed network channels. Does the NAE have 1250 capability?

  16. #16
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    Quote Originally Posted by dapper View Post
    It does look like the transceiver is the problem. My guess is that the NAE is FTTP-10. The baud rate is much higher on the TP/XF-1250. That is generally used for backbones or high speed network channels. Does the NAE have 1250 capability?
    I don't think so but Can I change the 1250 in Lonmaker or
    is the transceiver specified in the .xif file

  17. #17
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    2,062
    Post Likes
    Quote Originally Posted by mechinc View Post
    I don't think so but Can I change the 1250 in Lonmaker or
    is the transceiver specified in the .xif file
    The transceiver is hardware, normally it can not be field changed. You probably need to get a TP/XF 1250 to FT-10 router.

    Kevin

    Controls is a lifestyle not a job

  18. #18
    Join Date
    Feb 2008
    Posts
    225
    Post Likes
    Thread Starter
    The Mitsubishi board has a FT-10 chip in it.
    NAE needs FT-10 communication.
    Load the .XIF file and it shows up TP/XF-1250
    in the NAE.
    Used Echelon tool to look at the .XIF file
    and TP/XF-1250 shows up in the .XIF file.

    Called Mitsubishi tech support and they claim
    they only have one .XIF file for this unit and
    it is FT-10 communication.
    They sent it to me but still same issue.

    Any suggestions?

  19. #19
    Join Date
    Mar 2007
    Location
    New Castle, DE
    Posts
    99
    Post Likes
    Quote Originally Posted by poochz View Post
    The LNS tool can commission without a xif, but the NAE requires one. The easiest is to use Nodeutil to connect to the device and generate a xif file. Then just add the xif to the NAE as a resource.

    Nodeutil182 I believe is the latest, available free from echelon's web site.

    poochz
    Try to get the xif from the device

  20. #20
    Join Date
    Mar 2008
    Location
    Tennessee
    Posts
    128
    Post Likes

    Talking

    I agree with poochz and outofcontrolman you sould not even attempt an integration without nodeutil. once you understand how it works and you will never understand how you got along without it. Just because somebody from the manufacturer sends you an xif doesn't mean it was the right one, if you generate it yourself then there is no question. Anyway its free!!! and you can show off to your friends look how smart I am works great on the chicks too huh!!!!

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •