    Confused Carrier Rooftop Help

    I have a Carrier rooftop model 48HJD009 that I am getting an error code on.
    The error code is an induction fan problem. The induction fan run's all the time. Is there a problem in the motor speed sensor or is the control board bad?

  2. #2
    Join Date
    Nov 2004
    Posts
    240
    With the three-wire plug unplugged:
    With power applied to the unit, unplug the three-wire plug and measure the pins as follows:
    1. Connect the negative or black lead of the meter to pin three on the circuit board.
    2. Connect the positive or red lead of the meter to pin one.
    3. The meter should read between 7.5 and 10 volts DC.
    4. Move the red or positive lead to pin two. It should read between 21 and 24 volts DC.
    5. Replace the circuit board if these pins are outside these readings.

    With the three-wire plug plugged in:
    With power applied to the unit and the three-wire plug in place, measure the pins as follows:
    1. Connect the negative or black lead of the voltmeter to pin three on the circuit board.
    2. Connect the positive or red lead of the voltmeter to pin one.
    3. Slowly rotate the induced draft motor. On half of one rotation of the induced draft motor shaft the voltage reading should be less than 1 volt DC. On the other half of one rotation the voltage reading should be between 6.5 and 9 volts DC.
    4. If the voltage reading is not less than 1 volt DC on half of the rotation of the motor shaft and not between 6.5 volts and 9 volts DC of the other half of the shaft rotation, replace the Hall Effect Switch.
    5. Move the red or positive lead to pin two. It should read between 16.5 and 21 volts. If not, replace the Hall Effect Switch.

  3. #3
    Join Date
    Nov 2005
    Posts
    1,350
    Quote Originally Posted by djken View Post
    With the three-wire plug unplugged:
    With power applied to the unit, unplug the three-wire plug and measure the pins as follows:
    1. Connect the negative or black lead of the meter to pin three on the circuit board.
    2. Connect the positive or red lead of the meter to pin one.
    3. The meter should read between 7.5 and 10 volts DC.
    4. Move the red or positive lead to pin two. It should read between 21 and 24 volts DC.
    5. Replace the circuit board if these pins are outside these readings.

    With the three-wire plug plugged in:
    With power applied to the unit and the three-wire plug in place, measure the pins as follows:
    1. Connect the negative or black lead of the voltmeter to pin three on the circuit board.
    2. Connect the positive or red lead of the voltmeter to pin one.
    3. Slowly rotate the induced draft motor. On half of one rotation of the induced draft motor shaft the voltage reading should be less than 1 volt DC. On the other half of one rotation the voltage reading should be between 6.5 and 9 volts DC.
    4. If the voltage reading is not less than 1 volt DC on half of the rotation of the motor shaft and not between 6.5 volts and 9 volts DC of the other half of the shaft rotation, replace the Hall Effect Switch.
    5. Move the red or positive lead to pin two. It should read between 16.5 and 21 volts. If not, replace the Hall Effect Switch.
    awesome info
    I have also heard that the rf failure fault can be casued by this switch, is this true?
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  4. #4
    Join Date
    May 2007
    Location
    minnesota
    Posts
    29
    Thank you for your help, but I can not do the second part of this test be cause the induction fan is running all the time.

  5. #5
    Join Date
    Nov 2004
    Posts
    240
    Allstar - If pin 1 or 2 is grounded, under certain circumstances, you could get a code 8.

    jerrmey - You must not have a call for heat during this test. If your draft motor is running with no call for heat, check your safeties.

  6. #6
    Join Date
    Oct 2008
    Posts
    17
    I think most likely is the circuit board problem.