    pilot issue with Cozy space heater

    Inlaws basement space heater got the best of me.... I have a floor cozy heater with a Robert Shaw gas valve model 7000ASTR-4 with standing pilot with a push button spark pilot starter. Anyhow replaced the gas valve 2 years ago and new t couple last year, pulled and cleaned oriface and pilot.

    I manually light pilot with lighter hold it for 10 minutes to keep the pilot on. Adjust the pilot flame to high to keep a good flame on the couple. After a day or sometimes a week the pilot goes out? Check for down drafts and drafts in general nothing? Gas pressure is ok, I dont believe the t couple is bad after a year again, it tested ok. The unit has a spill switch with manual reset on the flue baffle in series with the t couple circuit. Every time i relight I test the circuit its OK. basement heater and its a PITA right now and its my inlaws units...
    “The price of anything is the amount of life you exchange for it.” – Henry David Thoreau

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    19,981
    Post Likes
    Kinda sounds like a venting issue. You should get a parts breakdown and an installation manual and see if the venting was installed correctly. I did one not to long ago, and the installer didnt install a baffle in the termination....or something lika that.
    It made the pilot go out all the time.
    “Now the freaks are on television, the freaks are in the movies. And it’s no longer the sideshow, it’s the whole show. The colorful circus and the clowns and the elephants, for all intents and purposes, are gone, and we’re dealing only with the freaks.” - Jonathan Winters

  3. #3
    Join Date
    Mar 2004
    Location
    midwest
    Posts
    995
    Post Likes
    Venting is sized ok, only about 8' total run into chimney in older clay chimney. If venting was an issue wouldn't the back draft safety trip causing the manual reset to trip? or are you talking about excessive draft too much? Never seen this with gravity vent system only down draft issues.

    Quote Originally Posted by coolwhip View Post
    Kinda sounds like a venting issue. You should get a parts breakdown and an installation manual and see if the venting was installed correctly. I did one not to long ago, and the installer didnt install a baffle in the termination....or something lika that.
    It made the pilot go out all the time.
    “The price of anything is the amount of life you exchange for it.” – Henry David Thoreau