    PMI Multistate Output

    Has anyone ever written to an enumeration point inside an FX controller from PMI ?
    I have an FX15 and the customer wants to be able to override the DO's from PMI. I need to be able to write a value of 0 for auto, 1 for on and 5 for off. Thank you in advance.

  2. #2
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    880
    For anyone interested, I figured it out. I used an MCO with an AOS as the slave. The AOS writes to a numeric writable in the FX and is converted to an enumeration for the override. Don't know if there is an easier way, but it works.