    We are looking into 5 Geothermal heat pumps. Do most commerial units come with controls and are they BACnet or Lon.

    Thanks

  2. #2
    Join Date
    Dec 2004
    Location
    SF Bay Area
    Posts
    605
    Post Likes
    I've done a couple different geothermal heatpump projects, and in each case, they all had low voltage controls (thermostat terminals), to which we applied our own DDC controllers.

  3. #3
    Join Date
    Mar 2008
    Posts
    86
    Post Likes
    I am commissioning a job next week with 29 heat pumps, they are not geothermal, and I have control of a cooling tower and boiler. Anyway I am using the Viconics HP stat. (Lon)

  4. #4
    Join Date
    Mar 2008
    Location
    Tennessee
    Posts
    128
    Post Likes
    probably will be brand specific the big manufacturers like trane or carrier will give you the option of factory mounted controls which will probably be a lon controller or a 24v interface to use somebody elses controls or just a themostat.

  5. #5
    Join Date
    Jul 2005
    Location
    Pittsburgh, PA
    Posts
    260
    Post Likes
    We have a couple of projects with Geothermal heat pumps, the PA Historical Commission loves these things. They have worked well in some cases and marginally in others, it all depends on well locations. They actually had problems with the wells warming in one case. The units came as previously mentioned, just 24V controls and you retrofit whatever you want. We have ALC on one job and JCI interfaced to ALC thru Modbus in the other.
    HotRod


    Controls..some days your a hero, some days your a zero. Direct acting since 1992.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •