    Someone please suggest me an alternative for TAC XENTA OP, Is there any option to switch from OP to some other display panel for control & monitoring and definitely supporting FT10.
    Lisboa, Portugal
    NY
    I used the L-VIS on a FT-10 network and it worked out pretty good. There is a bit of a learning curve to set it up but once you get the hang of it it's not too bad.
    May 2002
    If you want to get the LON variables out on this controller, the L-VIS works great. When you order it you can switch between IP852 or FT-10. It also has a built-in VNC server for remote operation from one user.
    The device can also be RNI for you and contains full AST functions with an email server.
    I'm the US rep so send off an email if you want more information.
    Pacific Time Zone
    Which OP are you talking about? The hand held OP or the touch screen?
    Also what does MAK mean in your subject line?
    Mak
    Crab, i am speaking about TAC Xenta Operator Panel, And sysint the main issue of switching from TAC Xenta OP to another display and control panel is: It goes quite expensive if clients asks for individual OP with every controller on standalone basis. You may imagine if i have 30-40 controllers with OP how much prices would be! I am kicked off.
    As stated by "Undercontrol" @
    http://hvac-talk.com/vbb/showthread....ighlight=L-vis, i agree i cannot bear to have expensive soluution.
    Sysint about which company you are speaking about, offering Lon devices?
    And Crab mak is "Mohammad Asif Khan" hope fits you.
    Pacific Time Zone
    Why not add a Xenta 511? You can get a lot more data and view it on any computer within the network and more.
    Also TAC Xenta series has at least two operator panels - The original OP and the OP1500.
    Pacific Time Zone
    3 - OP, OP7 & OP1500
    Pacific Time Zone
    I cannot attach the OP7. The file size is just above the limit.
    Also you could provide one/two of the low end OP's and just tell them to take it and plug it in where they need to; however, a 511 or different interface would be much, much better, unless the controller has an extremely simple program.
    May 2002
    Quote Originally Posted by makkhan View Post
    ...And sysint the main issue of switching from TAC Xenta OP to another display and control panel is: It goes quite expensive if clients asks for individual OP with every controller on standalone basis. You may imagine if i have 30-40 controllers with OP how much prices would be! I am kicked off...Sysint about which company you are speaking about, offering Lon devices?
    M Khan, I am the US Loytec rep. I suggest going directly to the Loytec web site for quote and information on product. You can download the LVIS configuration software and see what it takes to make graphics for LVIS and the LINX web server (same tool both devices, bacnet and LON)
    LVIS does the following:
    AST functions w/email
    VNC server built in
    Graphical touch
    RNI
    bacnet mstp / IP852 / CEA-709
    However, one touchscreen can satisfy many nodes of information plus you have VNC for some remote capability. Maybe this is helpful for you.
    LINX is the webserver. You can email me and I can also send some basic information for explanation. Since LINX makes web pages with the same free software as LVIS, you don't need any web language knowledge to create web pages.
    Feb 2005
    Quote Originally Posted by sysint View Post
    I understand that you are saying you can use the free tool to make webpages on LINX, but how many pages and how much datapoints.
    Also how does the L-Web tie into all this?
    May 2002
    Amigo, The LINX is much like the JACE in that capacity is tied to use. Schedules, Trends, etc... take up space so that plays into things. Also, by design the LINX automatically creates OPC tags out of everything. By extension this means that structured variables become multiple individual OPC tags. I could recite some design data, but I'd rather count on some actual field information. Since they link together the short answer is if you run out of space you can get a second box... I'm working on practical limitations now.
    * Hosts customized pages with dynamic content
    * Supports trending, scheduling, and alarming locally
    * Alarm notification via e-mail
    * Embedded OPC XML/DA server fully compliant with the OPC XML/DA standard
    * Supports up to 1000 OPC data points
    * Built-in Web server for device configuration
    * SNTP support for time synchronization
    * Built-in communication test
    * Status and activity LEDs
    * OPC status and activity LED
    * Network statistics information accessible through OPC data points
    * 12-35 V DC / 12-24 V AC supply voltage
    * 105 x 86 x 60 (L x W x H in mm) i.e. 6 TE
    * DIN-rail mountable
    LWEB 800 is a free .net application. Basically it is a free browser. It has some nice features. You can make skins and also give it a widget-like look if you want (I liken it to some of the things that Vista does on PC's). Next step up is utilizing LWeb 801 is basically a tool to enable archive data logging for multiple LINX devices.
    The concept is growing on me because it doesn't matter bacnet or LON you move to the OPC tags and there is your enterprise application or you can work within the LINX boxes and utilize local visualization and AST functions.
    To compare, Tridium creates their own framework, Loytec lets you use your config tools and also lets you use whatever OPC platform on the other side. So, if you are enterprise you aren't tied to Loytec for everything, and if you are not utilizing enterprise you can link the Loytec servers without buying training, licensing, sales quotas etc... (NOTE to Trid guys: I'm not saying one is better than the other method, just different)
    M.Khan
    Crab, 511 means going on ethernet, and what i need is a local display for standalone system. Op1500 & OP7, i am looking at it and have requested to check prices.
    Over here in Pakistan, Consultants, Contractors and end-users they do only what they were taught to do and perform. Here people are not well aware of the advance technology, even if you try to convince them that 1 display is enough for the whole system they would never agree. They want only what they have written in there specs.
    Also, HVAC controls is managed by the technicians after handover and they want the system like a piece of cake to handle. Consequently, they need ease of work, if standalone they want every single display panel with each controller. they don't want to surf through the display (like in Tac OP), what they need is a display same like in DX9100 & FX controllers by JC. I am sure you have worked on that or atleast you know.
    So this is the situation, if i go for 40 OP's i am a dead man. This is the purpose i was trying to check if any freely programmable display or something like that available in the market which coould be cost effective and be able to manage the AHU or whatever.
    Sysint, thankyou for the advise i would definitely check the prices and would download the software, in case i will come back to you.