    Cooling tower VFD Min Speed

    What is the manufactors min speed/HZ on a cooling tower fan motor rated for inverter duty. I was taught 20hz was min speed to keep from over heating. Engineer wants to run with no minimum.
    "Dying aint much, its living thats hard." (Josey Whales)

  2. #2
    Join Date
    Mar 2008
    Location
    Indy
    Posts
    378
    Post Likes
    I set fan applications at 10 Hz and pumps at 18 Hz on the drives I set up. I've had no reported problems after ten years of factory start ups.
    If this cooling tower is belt driven, I wouldn't go below 6 Hz or 10%.
    If it is gear driven, you can't go below what the gear drive manufacturer recommends what the min. speed should be for proper lubrication.

  3. #3
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,133
    Post Likes
    Was told by Marley that at 18hz your airflow pretty much stops thru the tower. I run the tower water up to 2F below setpoint before sending the drive a run command. Starts at 18hz and goes from their. If it drops 4F below setpoint the drive goes off. The towers and drives I just installed run within
    .15F of setpoint and usualy closer to .04F.
    Last edited by absrbrtek; 10-20-2008 at 06:00 PM.
    To much work with too little time!!!!

  4. #4
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Post Likes
    Still did not teach you anything! 20HZ is safe but I would contact the tower box rep. Some of the boxes have a slinger for "splash" lubrication. Don't work so well at slow speeds. The motors require around 20HZ to get the fans on the rear to effectively cool the motor. TEAO might need more speed since they use ambient air over them.
    "I'm from Texas, what country are you from?"

  5. #5
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,133
    Post Likes
    LOL, that's what Marley recommended. Been online for a few 1000 hours with no issues.
    Quote Originally Posted by stickerhead View Post
    Still did not teach you anything! 20HZ is safe but I would contact the tower box rep. Some of the boxes have a slinger for "splash" lubrication. Don't work so well at slow speeds. The motors require around 20HZ to get the fans on the rear to effectively cool the motor. TEAO might need more speed since they use ambient air over them.
    To much work with too little time!!!!

  6. #6
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    364
    Post Likes
    Thread Starter
    Quote Originally Posted by stickerhead View Post
    Still did not teach you anything! 20HZ is safe but I would contact the tower box rep. Some of the boxes have a slinger for "splash" lubrication. Don't work so well at slow speeds. The motors require around 20HZ to get the fans on the rear to effectively cool the motor. TEAO might need more speed since they use ambient air over them.
    Dident learn anything from you 20 years ago when you was my supervisor why should anything be different today? Hhhhmmmm is it me or you???????
    "Dying aint much, its living thats hard." (Josey Whales)

  7. #7
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes
    I would agree with the a 20HZ min. for that application , any new inverter start ups on pumps or ahu's I would set up for 15HZ to 20HZ and have had no problems at all.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  8. #8
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Post Likes
    Quote Originally Posted by CaptJackSparrow View Post
    Dident learn anything from you 20 years ago when you was my supervisor why should anything be different today? Hhhhmmmm is it me or you???????
    That's why you live out in nowhereville where no one knows what you are doing is right or wrong. That's why C-alvin made so much $$$
    "I'm from Texas, what country are you from?"

  9. #9
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    364
    Post Likes
    Thread Starter
    Quote Originally Posted by stickerhead View Post
    That's why you live out in nowhereville where no one knows what you are doing is right or wrong. That's why C-alvin made so much $$$
    Well thats what I like about it! I get to decide what is right and what is wrong! No corprate policy or little Hitlers! Its right if I say its right and wrong if I say its wrong. Like the little trip to "trailer hill", That was WRONG!
    "Dying aint much, its living thats hard." (Josey Whales)

  10. #10
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    364
    Post Likes
    Thread Starter
    Thanks for the replies. I set min at 15hz as the know it all engineer agreed to. Its his motor!
    "Dying aint much, its living thats hard." (Josey Whales)

  11. #11
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Post Likes
    Quote Originally Posted by CaptJackSparrow View Post
    Well thats what I like about it! I get to decide what is right and what is wrong! No corprate policy or little Hitlers! Its right if I say its right and wrong if I say its wrong. Like the little trip to "trailer hill", That was WRONG!
    Whoo! You just slapped my brain! I thought you would have wanted to have forgotten that! Bad mental picture but it was funny! I will see if C-alvin remembers!
    "I'm from Texas, what country are you from?"

  12. #12
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    364
    Post Likes
    Thread Starter
    The question is not if you can remember but if can you forget!
    "Dying aint much, its living thats hard." (Josey Whales)

  13. #13
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Post Likes
    Quote Originally Posted by CaptJackSparrow View Post
    The question is not if you can remember but if can you forget!
    I was innocent but you and Tio wern't
    "I'm from Texas, what country are you from?"

  14. #14
    Join Date
    Mar 2007
    Location
    State of Confusion
    Posts
    1,225
    Post Likes
    Don't let the Mods see you fighting like this.

    haha play nice..

  15. #15
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Post Likes
    No fighting here. We been buds for along time. Just a "thing" that happened in the past so we will shut this one down and get back to the original post. I became a "thread high jacker" Absrbrtek, don't baned me please! LOL
    "I'm from Texas, what country are you from?"

  16. #16
    Join Date
    Mar 2007
    Location
    State of Confusion
    Posts
    1,225
    Post Likes
    Can I ask a question here? Why not let it go to 0? Why run a motor without purpose. Isn't the most efficient motor, a motor that isn't running? 0 power consumption. It's a soft start, so locked rotor amps isn't a issue. Maybe I'm way off on this one too.

  17. #17
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    489
    Post Likes
    Quote Originally Posted by maxpower View Post
    Can I ask a question here? Why not let it go to 0? Why run a motor without purpose. Isn't the most efficient motor, a motor that isn't running? 0 power consumption. It's a soft start, so locked rotor amps isn't a issue. Maybe I'm way off on this one too.
    Even VFD rated motors have minimum speed ratings for the most part. There are multiple issues. Cooling of the windings, lubrication of the bearings, and probably a few others. Yes you could go from 15-20hz straight down cycle off. The invertor electronics probably take some extra heat on each start stop though, so there are trade offs.

  18. #18
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    364
    Post Likes
    Thread Starter
    I came up with some Baldore info that gave a ratio of 20to1 for Emotors and 1000 to 1 for super E motors in a variable torque application. I did not understsnd the ratio or what it meant. The way I see it is it depends on the application were like a cooling tower fan is heavy and takes some torque to get it and keep it moving. If the application has less torque requirement we could slow it down more the more the low speed torque requirement the higher the min speed. ???

    The Baldor specs said something about the motor having full torque all the way down to 0 hz but I watched the amps on a 20 HP motor at 20 amps at a 5HZ output on the drive.
    "Dying aint much, its living thats hard." (Josey Whales)

  19. #19
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    364
    Post Likes
    Thread Starter
    Oh by the way StickerBritches it a belt driven tower.
    "Dying aint much, its living thats hard." (Josey Whales)

  20. #20
    Join Date
    Sep 2008
    Location
    Delaware
    Posts
    243
    Post Likes
    You probably do not want to go much below 20 Hz for a prolonged period. Motor cooling can become a real issue at speeds lower than that.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •