    cvhf910 ch530 problem

    Went to a site today to do the winter maintenance on a couple of chillers and found both chillers the hour and start meters have zeroed themselves along with the purge minutes. The customer had a power bump a week ago but other than that there has been power applied to these chillers ever since start up except for servicing not that that matters. I hooked up my laptop and still reads 0. I checked for settings that allow zeroing etc I got nothing . I am stumped. I am waiting for a response from tech support but as it was late in the day I expect to hear from them tommorrow. Any ideas guys?????

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    from CTV-SVB31B-EN:

    "Problem 1): MEMORY LOSS: This software contained a flaw that caused a
    sector of the memory to be written excessively. This action caused a portion of the EEPROM memory to become corrupted. Once corrupted the failure
    surfaces each time a power interruption occurs (greater than a couple of seconds) causing the data in EEPROM to be recalled to active memory. The corrupted portion of the memory includes the starts and hours count (set to zero), the historic diagnostics (lost), and Setpoints (set to default levels). The unit will restart and run with the default Setpoint values, however, they will need to be re-entered as necessary.

    Problem 1 is addressed with version CTV 9.0. (This version CTV 9.0 does not
    fully address problem 2 below)"

    basically...upgrade the software.
    of course, by now the software version is up to 10.02

    there is a confidential service bulletin (i can't publish anything about that!). what serial number do you have? they list the units that need to be upgraded.

    good luck.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. #3
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    Thread Starter
    Jayguy thanks I can't access my trane acct for some reason it isn't working for me.

    sn L05M05543 and
    sn L05M05541

    Let me edit my info in my profile to include my email. Would you mind sending it to me I would really appreciate it. I am 8 hrs from home on a holiday and no one from my office is answering. While I am at it can I reset the hours and starts to what they were at my last inspection? I haven't looked at that yet bit of an afterthought. A simple yes or no will do on that one I can figure out the rest. Thanks
    Last edited by mustardman; 10-14-2008 at 01:42 AM.

  4. #4
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Yes you can edit the hrs in the newer software . Graham. good luck
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  5. #5
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    285
    Post Likes
    If you are a trane tech, Take a look on the back page of the Sept/Oct 2008 technician newsletter.

  6. #6
    Join Date
    Nov 2004
    Location
    North Florida/South Georgia
    Posts
    1,038
    Post Likes

    You Trane guys kill me:)

    I don't understand why you guys get on here & talk in riddles.

    Wouldn't it be easier just to call each other? Afterall, the riddles don't help the rest of us dum dums. But, they are occasionally entertaining.

    For the record, I'm not a Trane tech, but I want to know whats on the back of the news letter.
    All my leon freaked out!

  7. #7
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    SssssssHhhhhhhhhhhhhhhhhhh. your not suppost to give away the new corporate handshake or tell anyone about the new tattoo we all have to get . Its meant to be a secret shhhhhhhhhhhhhssssssssssss dont tell ??????????
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  8. #8
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    Thread Starter
    Quote Originally Posted by jimbob73 View Post
    If you are a trane tech, Take a look on the back page of the Sept/Oct 2008 technician newsletter.
    Will do as soon as I get home I am 8 hrs from there right now. An hour or so I after my last post got on to the portal and got everything I needed all is better now. Thanks everyone for there help as always it is much appreciated.

  9. #9
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    285
    Post Likes
    chiller mekanik, Because there are people on here with too low of a post count that could do harm to themselves and others if they had the info

    I'm being sarcastic, Due to some of the stuff I've been reading around this place. As long as I post a hundred topics in the funny forum, Then ask one question for info, I guess I would have earned the right to get it. But if I have 30 years experience and have 2 posts and ask for info, I'm SOL!

  10. #10
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    285
    Post Likes
    Quote Originally Posted by mustardman View Post
    Will do as soon as I get home I am 8 hrs from there right now. An hour or so I after my last post got on to the portal and got everything I needed all is better now. Thanks everyone for there help as always it is much appreciated.

    You were on a job 8 hours from home?

  11. #11
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    Thread Starter
    You betcha our territory is huge main office out of Vancouver BC but I work in the interior out of the Kelowna office. I go as far as a town called Dawson Creek its about 1100 kms from my place in Vernon. Google it. BC is very big. A lot of windshield time because our towns are very spread out and none of them are big enough to support a guy full time. I am in Prince George in my hotel as we speak about 750 kms from my front door. I am on the road 1-2 weeks a month year round but its not too bad the more time I am away from home the less chance I have of ticking off the wife.
    Last edited by mustardman; 10-14-2008 at 10:06 PM.

  12. #12
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    285
    Post Likes
    Geesh, In the midwest, USA, There are Trane offices all over the place so a job 3 hours away is considered a haul.

  13. #13
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    Thread Starter
    It used to be like that for me prior to transferring from the Vancouver office but now I am just glad I don't pay the fuel bill. The only real downside is you have to quadruple check everything before you head out nothing worse than forgetting a part only to discover it when you get to site around 10pm or something. Not that that has ever happenend to me

  14. #14
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    285
    Post Likes
    You are one dedicated Trane citizen!

  15. #15
    Join Date
    Nov 2004
    Location
    North Florida/South Georgia
    Posts
    1,038
    Post Likes
    Quote Originally Posted by jimbob73 View Post
    chiller mekanik, Because there are people on here with too low of a post count that could do harm to themselves and others if they had the info

    I'm being sarcastic, Due to some of the stuff I've been reading around this place. As long as I post a hundred topics in the funny forum, Then ask one question for info, I guess I would have earned the right to get it. But if I have 30 years experience and have 2 posts and ask for info, I'm SOL!
    I hear you loud & clear. I spend time myself wondering about the ill effects from some of the information we post on here when it gets in the wrong hands; ie, people without the proper experience.

    No doubt there have been times people have read something on this web site & went to work the next day claiming to have a "revelation" and now they know what to do to fix the problem. I'm sure there have also been occasions when someone has misapplied something read here only to compound the problem & likely cost someone some money.

    That being said, as we (pro's) help each other out from time to time, you have to wonder how much injustice we do when our posts are read by incompetant people.

    I know you guys are factory & I have no problem with that & I'm sure you know by now I'm independent (always have been) & I have no doubt that you don't have any problems with truly competant independents.

    For instance, a Trane tech may have plenty of information that he would like to gaurd for a variety of reasons. But, if your on a forum & someone in another part of the country needs help & you are confident that this person knows what he is doing, you would probably be inclined to help.

    There could be a day that you wind up in front of a Carrier machine & who knows, maybe one of the lowly independents could possibly be able to help you out. It would be no different than a Trane tech giving specific info to a McQuay tech that is working on a Trane chiller. Unless of course all of the factory guys on here have a problem with independents. But in all honesty, I would be suprised if that was the case.

    I know this has been kicked around before, but maybe its time we start another thread to see what kind of support we could scrounge up & really think about approaching the Moderators to consider a forum just for chillers mechanics. How would we determine elegibility? I'm not completely sure but, one thing that comes to mind is maybe there could be a committee that could vote on membership requests. Or, we band together & come up with a reasonable list of requirements that mods would ask people to produce when they request clearance for the "chiller" forum.

    Maybe we would even want to consider operators participation if they have the appropiate skill sets. Now, before any of the competant operators get offended, I'm not talking about excluding you. I'm talking about excluding the guys that don't approach from delta T.

    Another idea is that apprentices could possibly join if a member in their area recommends them.

    I suppose this could be a pipe dream. But, if anyone thinks its a good idea, lets start another thread & see where it goes. If we get enough support, maybe the Mods would consider it.

    One more thing, I know one of you guys can tell us whats on that news letter. C'mon, share a little gossip. (unles it really is boring)
    All my leon freaked out!

  16. #16
    Join Date
    Oct 2006
    Posts
    77
    Post Likes
    I could tell you, but then I would have to kill you.


    It just says to use CTV MP Ver 10.0 instead of 10.02 due to some bug.

    Pretty cool huh.
    Trane service, and Supertek65 fan club president, midwest chapter

  17. #17
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    285
    Post Likes
    Quote Originally Posted by hvacowboy View Post
    I could tell you, but then I would have to kill you.


    It just says to use CTV MP Ver 10.0 instead of 10.02 due to some bug.

    Pretty cool huh.
    Bug, What bug? I was referring to the right gloves for the job part.

  18. #18
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    2,096
    Post Likes
    I overhauled a sidewinder in Prince George with the Jer and did the controls upgrades on the chillers at the university.

  19. #19
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    Thread Starter
    I will guess the sidewinder you refer to is the canada trust building with good ol Bob as the operator. I think thats the only one. What University the college of new cal or UNBC cause if its the latter thats where I was having my problem hauled that old absorber out of there a few years ago and put in 2 CVHF 910's. Time for another retro fit on the controls at new cal I think it will soon be CH 531 happening in there. Lots of machines up here are needing to be upgraded I think we are going to overhaul the PCV at the hospital just waiting for a PO. I think I will be spending a lot of time up here over the winter.

  20. #20
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    2,096
    Post Likes
    Yes, it was the bank and the upgrade was the PCM's on UNBC.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •