    Commercial Kitchen Vent/HVAC issue

    Inspected a local brew pub with some unusal HVAC/venting issues that I would be interested in a professional opinion on.

    On humid days (and only during hot humid days) they have some water leaking from ducts and venting equipment. The worst location is the basement kitchen (huge commercial set up with 4 cooktops, 2 fryers, etc). Although I did not observe it, I am told that so much water was dripping from the vents that they had to rig up a makeshift gutter to run the water to the sink. It seems logical to me that since it only occurs on days when teh exterior air is humid that the issue must be related to the make up air system (a huge commecrial unit on the 5th story roof) but I am seeking professional thoughts on that..... There were some small (4 square inches) holes in teh duct work running from the intake unit on the roof down to the kitchen, but these did not seem large enough to account fo rthe mass quantities of water the manager decribes.

    Other locations of dripping: The HVAC vent at the top of the stairs (possibly condensation from teh heat of the kitchen rising up?); A bathroom HVAC vent (located pretty far from all other concerns, but adjacent to the exterior brick wall and in a fairly isolated section of a large restaurant bathroom with 15 foot ceilings); and two exposed metal HVAC ducts at the front entry (possibly from entry air mixing with the greenhouse effect of the enormous picture windows).

    Any thoughts? Incidentally they have had 3 contractors out to look at the HVAC system (not the kitchen venting and make up air, though, for some reason) and they could not identify the problem. Also, the brew room is totally sealed off from teh rest of the place with its own HVAC systems.

    I welcome your input as I would like to offer some suggestions for the frustrated owners.....

  2. #2
    Join Date
    Oct 2001
    Location
    Comstock Park Michigan
    Posts
    100
    Do the RTU's have traps installed, if not they will definitely not drain properly and will probably overflow the drain pans on humid days. May not be the problem but worth checking first.
    We do it nice cause we do it twice!

  3. #3
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    805

    Lightbulb

    Need more information...

    Average indoor temps and humidity?

    Is the duct work exposed ?

    Is duct work metal duct?

    Is duct work insulated or not ?

    Infiltration outdoor air making its way inside?

    Hood system not balanced causing negative pressure?

    ect...ect...ect
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  4. #4
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    487
    What is the discharge air temp? If too cold the ductwork insulation will be inadequate. Several things might cause a drop in the DA temp. Dirty coils, dirty filters, worn sheaves, all will lower air flow causing the discharge air temp to drop. I'ld bet one of the above, but it could be someone has made changes and caused the problem by trying to get more cooling.

    If the space humidity is abnormally high that would contribute too.

  5. #5
    Quote Originally Posted by bob_scheel View Post
    What is the discharge air temp? If too cold the ductwork insulation will be inadequate. Several things might cause a drop in the DA temp. Dirty coils, dirty filters, worn sheaves, all will lower air flow causing the discharge air temp to drop. I'ld bet one of the above, but it could be someone has made changes and caused the problem by trying to get more cooling.

    If the space humidity is abnormally high that would contribute too.
    Thanks, Bob.

    I think those things have been checked, and they may be responsible for the upper restaurant issues (I think teh heat and humidity from teh kitchen contributes to condenastion at one register, while the huge picture windows and entering customers may contribute to teh other problem). I will have to recommend cleaning of the items you suggested and a primer course for employees on humidity and cooling systems ("don't touch the freaking thermostat!")

    How would that all apply to the waterfall (indoor rain seems accurate from their description) at the hood vent? I can see that high temps exist there, but it would seem that the humidity should be sucked out, not condensing there.... And the fact taht it only is noted when it is humid out keeps me wondering about any role the make up air plays in this (since I can't see how else any humid air is getting from outside into a basement kitchen.)

    thanks again

  6. #6
    Join Date
    Feb 2007
    Location
    Northern Ontario
    Posts
    128

    Talking

    If they condition the make up air to the kitchen Ive seen this done the air is dumped at the front edge of the hood this cold air below dewpoint is hitting sufrace causing zone where humid air in kitchen condenses ..... I see this in the winter here when the restaurant doesnt want to heat the fresh make up air the cool outdoor air is causing same situation..... good luck

  7. #7
    Quote Originally Posted by skpkey9 View Post
    Need more information...

    Average indoor temps and humidity?

    Is the duct work exposed ?

    Is duct work metal duct?

    Is duct work insulated or not ?

    Infiltration outdoor air making its way inside?

    Hood system not balanced causing negative pressure?

    ect...ect...ect
    Good questions - I don't have the answers to all....but here are some ballpark answers which may help you.

    Average indoor temp is a steady 70 (that's what they have it set at) for the restaurant area. The kitchen is WAY hotter than that (it was over 90 on a 60 degree day) and even hotter over teh cooktops (where the major problem exists).

    Duct work is only partially exposed (the exposed parts are metal) while most seems insulated (does not appear metal, but I only got a limited look through some registers).

    Air infiltration is likely (since this only occurs when it is humid out - as opposed to hot but not humid), but only through the front doors (when customers come in) or through the make up air duct (insulated, not metal BTW).

    I am not sure if the hood balance has even been checked.

  8. #8
    Join Date
    Dec 2008
    Location
    New York
    Posts
    5
    Was this ever resolved, I am curious as my thought process is the make-up air is traveling 5 floors to the kitchen. If it's traveling around 1000 or less fpm amd it should be. Make-up air is volume, not necessarily velocity. If it is traveling slow, then it would have lots of time to cool and condensate. I didnt notice it anywhere, but is the MUA duct insulated. If not, it has 5 stories to travel and cool down. Just a thought.

  9. #9
    Thanks, hoodguy - no, it has not been brought to a complete resolution yet, largely because we have not been able to replicate the conditions in winter and there is some disgreement from the installer about the theory that the make up air humidity is not being adequately addressed. We can't test it (no real summertime type humidity) so we are at a bit of a stalemate, which I expect to continue into spring/summer.

    I appreciate everyone's thoughts and input, though and will post the result if/when we get one.

    Incidentally, yes the MUA duct (all 5 sotries of it) is made of insulated duct. The thought of cooling and condensing over 5 floors of travel is one I will incorporate into our discussion. Thanks!