Economizer? Yeah or Neah?
I'm putting two five ton rooftop units (nordyne 14seer duel fuels) in a small bar / music venue. Is it worth it to get an economizer? My concern is that a big problem with high capacity spaces is humidity. When the economizer kicks fully on, will the lack of an operating AC (since the economizer takes over) create humidity problems?
-
10-13-2008, 04:06 PM #2
Can happen. Best bet is get an enthalpy control instead of just dry bulb temp changeover so if cool but humid, you don't economize. Some units will do stage 1 as economizer and stage 2 as compressor in case the economizer alone can't do it. Not sure how Nordyne does it.
-
10-13-2008, 05:00 PM #3
Professional Member
- Join Date
- Mar 2003
- Posts
- 7,249
single enthalpy can cost you in both comfort and economy. Use a comparative enthalpy control if you choose to economize.
-
10-13-2008, 05:47 PM #4
Suggestion set up the economizers on ventilation on demand using CO2 as your base. It would solve several problems at once. Here is a link to a white paper that was written on a job I did a few years back over seas.
http://www.genesisair.com/documents/...akesforIAQ.pdf
-
10-13-2008, 10:49 PM #5
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
single or dual point enthalpy is the way to go. Most cities require economizers
on anything over 2 or 3 tons anyway. They can save big $ and create a comfortable space.I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!