  1. #14
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,725
    If it was me I wouldn`t help him out .It`s obvious he doesn`t want any he hasn`t answered the important questions. He want`s info handed to him without doing leg work.

    Nice to see you back carriermechanic.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  2. #15
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    373
    ent. cond. = 82.3
    lvg. cond. = 91.6
    SDT = 93.1
    delta P = 5 (46 psi in 41 psi out one gauge used 1# increments 0-60 range)

    ent. cool. = 54.7
    lvg. cool. = 45.2
    SST = 44.3
    delta P = 5

    drive locked @ 60Hz
    amp probe in starter reading = 454amps which is 79.5 amps
    FLA = 571 and screen reads 80% 456amps
    guide vanes where wide open

  3. #16
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    373
    Now i was not the mechanic on site that took the readings i had to get them today from him but he is much more experienced then i. and has 18 years with carrier but left about 5 years ago so i trust his readings. he also said that they put an eductor in the skimmer line not sure why that would be needed but they must have had a problem skimming. sorry i for the wait on the readings. im in a rush so i hope i didn't forget anything. o yeah the chw setpoint is 42.

  4. #17
    Join Date
    Jan 2007
    Posts
    13
    Quote Originally Posted by carriermechanic View Post
    I have not been with carrier for 29. I have only been with them for 10. And I 100% agree that he needs to get one of us out there. I am just saying what I think it might be from what I have seen starting up xrv's and installing vfd's on xr chillers. I am just letting people know what I have seen. They can do whatever they wish with that information. It would be nice to have some data as far as a good log of the machine when it is operating. Giving us different temps and load % will help a lot. Let us know what they find.
    It dont matter if you been with Carrier 10 years or not, sometimes its not good to give Carrier advice to somebody else to work on a chiller under warranty. And by the way the extra eductor is for low speed, light load oil recovery.

  5. #18
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    373
    this is in the line from the cooler to the vane housing , never heard of one in that location before.

  6. #19
    What are your initials chlorfree??? I am sure we now each other. Anyway, I guess I can't help you DITAW. I know what the problem is. Hopefully your carrier guys can figure it out. Good to see you to goodlistener.

  7. #20
    Join Date
    Aug 2000
    Location
    USA
    Posts
    4,995
    Interesting train of thought.
    Quote Originally Posted by carriermechanic View Post
    What are your initials chlorfree??? I am sure we now each other. Anyway, I guess I can't help you DITAW. I know what the problem is. Hopefully your carrier guys can figure it out. Good to see you to goodlistener.
    Your poor planning does not constitute an emergency on my part!!!!

  8. #21
    Yeah, I guess it is.

  9. #22
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,864
    Did anyone run the vane calibration?
    God Bless our Veterans

    God Bless the USA

  10. #23
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    371
    Looks like you have a .2KW per ton machine. Carrier will return to the top of the heap now!
    "Dying aint much, its living thats hard." (Josey Whales)

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event