    19xrv won't load

    have a newly installed xrv that will not load above 80 percent , locked drive at 100%, flows are good, tubes are clean, around one degree approach on cooler (at 80%), vanes are calibrated and checked. vanes wide open still only 80 percent load on motor. its still under warranty so it is not really my issue but i am still curious , besides i don't have a lot of faith in the local carrier office most of there techs now work for the same company as me.

  2. #2
    Join Date
    Jan 2005
    Posts
    604
    So, does it need to load up more than 80%
    Is there issues with not making setpoint?
    Are vanes actually 100% open?

  3. #3
    Join Date
    Apr 2007
    Posts
    177
    Quote Originally Posted by DITAW View Post
    have a newly installed xrv that will not load above 80 percent , locked drive at 100%, flows are good, tubes are clean, around one degree approach on cooler (at 80%), vanes are calibrated and checked. vanes wide open still only 80 percent load on motor. its still under warranty so it is not really my issue but i am still curious , besides i don't have a lot of faith in the local carrier office most of there techs now work for the same company as me.
    what is your motor speed, when the motor goes over 42hz the guide vanes go to the full open position I belive the default setting for the max guide vane opening is 80 %. Does the load warrant going to 100#?

  4. #4
    Join Date
    Sep 2008
    Location
    Mesquite Tx.
    Posts
    374
    Is it making design tonnage?

  5. #5
    First of all u need to go into the service menu and set your guide vanes to no more than 70%. Was the drive installed on an older xr or did it come with the chiller? Check to make sure that the drive is at 60 HZ and the guide vanes are fully open. If both of these check out then you need to change your CT ratio in the ISM. But you need to make sure that both the guide vanes are all the way open and the motor is at 60 HZ.

  6. #6
    Join Date
    Feb 2007
    Location
    Baltimore MD ( Balimer, Murilyn)
    Posts
    140
    First of all if the machine is under warranty, Carrier should have been called before you mess with the machine. There's nothing worse than trying to troubleshoot a unit that someone else has monkeyed with.
    Second, I don't understand your statement you don't have any faith in the Carrier mechanics because they work for the same company as you. Does this mean you work for Carrier? Does this mean they left Carrier and now work for your company?
    I know one of their mechanics and their field engineer. I have complete faith in both of those individuals.

  7. #7
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    369
    not messing with chiller still under warranty just curious if any one ever had this issue to me it seems to be something other than the vanes. maybe wrong imp or something with the motor. i have heard of a machine with the wrong imp before and to answer the question about the mechs from carrier the jumped ship. dont know the mechs from carrier that are still there personally so i should'nt talk about there ability.

  8. #8
    Join Date
    May 2006
    Location
    N.E. IA
    Posts
    512
    When I worked for Carrier starting up new chillers, I would occasionally come across this same situation. Sometimes not even able to get 70% amperage draw, but still getting required chilled water temperature drop at design flows. You need to make sure you have design conditions on ALL fronts..... Chilled Water flow, chilled water temperatures, condenser water flow, condenser water temperatures. etc. etc. Anything lower than design temperatures and flows will result in less than full load amperage draw.
    "Wheel" mechanics work on "Wheel" chillers

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event