    Carrier 19XR Tower Water Control

    We're having surge problems with a 300 ton 19XR. I was told that the tower water needs to be reset according to load. We don't get actual demand as an input to the BAS system, so I'm using evap temp drop.
    I've programmed the following reset:
    3* (min) Evap Delta T = 65* tower water set point
    12* (design) DT = 85* tower water temp set point
    Does this sound like I'm on the right track?
    TIA,
    jogas
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  2. #2
    Join Date
    Jan 2005
    Posts
    604
    That may work for ya. Not ever done it that way before.
    How about % motor current, as the basis for reset?

  3. #3
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,720
    Quote Originally Posted by Carrene #2 View Post
    That may work for ya. Not ever done it that way before.
    How about % motor current, as the basis for reset?
    I don't think we get % amps into the BAS system either.
    Is this reset strategy/setpoints correct for this chiller?
    jogas
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  4. #4
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    371
    I would also like to see some guidlines to contol tower water temp on Trane VFD chillers with generic BAS as well. I think Tracer Summit has a canned program for this but is there any Trane publised condenser water temps at a given load or is it based on reducing Delta t between chill water and condeser water temp to reduce overall lift at reduced load. What does York base cwt on?
    "Dying aint much, its living thats hard." (Josey Whales)

  5. #5
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,820
    I hope your set points are adjustable.

    God Bless our Veterans

    God Bless the USA

  6. #6
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,720
    Quote Originally Posted by CaptJackSparrow View Post
    I would also like to see some guidlines to contol tower water temp on Trane VFD chillers with generic BAS as well. I think Tracer Summit has a canned program for this but is there any Trane publised condenser water temps at a given load or is it based on reducing Delta t between chill water and condeser water temp to reduce overall lift at reduced load. What does York base cwt on?
    I was wondering the same thing.
    Load driven reset verses a CHW (Evap Pressure correlation) / CWT (Condensor Pressure correlation) reset. Yeah, it would have to be constant volume, which this 19XR is.
    But.....at least on this 19XR, CHW delta always equals CWT delta.
    Lastly, on this 19XR, discharge pressure drives the oil return eductor, so proper head pressure is important.
    I'm hoping some Carrier 19XR Guru's will chime in on this.
    jogas
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  7. #7
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,720
    Quote Originally Posted by Randy S. View Post
    I hope your set points are adjustable.

    I hope you can give us a complete, insightfull contribution to this discussion
    Are you saying the reset set points are wrong?
    Or will they have to be changed on a regular basis?
    jogas
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  8. #8
    Join Date
    Apr 2007
    Posts
    177
    Quote Originally Posted by jogas View Post
    I hope you can give us a complete, insightfull contribution to this discussion
    Are you saying the reset set points are wrong?
    Or will they have to be changed on a regular basis?
    jogas
    If the machine is a 19XRV set the tower control to maintain 20 degrees above chilled water setpoint. If the machine is a fixed speed machine what I have found that setting the tower control to maintain a condenser water at 68 to 72 degrees entering the machine works well, have you thought about letting the PIC control the tower water through the ISM and settings on the PIC. The ISM control outputs a 4-20ma signal to operate a valve or a VSD on the tower.

  9. #9
    Are you not suppose to keep your 10,10,10 rule so you maintain your 60-70 degree lift ?

  10. #10
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,720
    Quote Originally Posted by slb8101 View Post
    If the machine is a 19XRV set the tower control to maintain 20 degrees above chilled water setpoint. If the machine is a fixed speed machine what I have found that setting the tower control to maintain a condenser water at 68 to 72 degrees entering the machine works well, have you thought about letting the PIC control the tower water through the ISM and settings on the PIC. The ISM control outputs a 4-20ma signal to operate a valve or a VSD on the tower.
    Thanks for the reply.
    It is a fixed speed machine. We've tried fixed set points 72*-78* and still had surge problems. The machine has a fixed 44* CHWS set point. So it should be a constant 64* tower water set point? That seems low, doesn't it?
    Also, what is the 10-10-10 rule?
    jogas
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  11. #11
    Join Date
    Apr 2007
    Posts
    177
    Quote Originally Posted by jogas View Post
    Thanks for the reply.
    It is a fixed speed machine. We've tried fixed set points 72*-78* and still had surge problems. The machine has a fixed 44* CHWS set point. So it should be a constant 64* tower water set point? That seems low, doesn't it?
    Also, what is the 10-10-10 rule?
    jogas
    The twenty degree rule is for the varable speed machines, normally 72-78 degree tower water with a fixed setpoint you should not have a surging problem. Iwould be looking at the cleanliness of the tubes both cooler and condenser, refrigerant charge,linear float metering device. possibly air in the machine from the factory i saw a few of those machines slip out of the factory with non condensibles still left in the system.

  12. #12
    Join Date
    Apr 2007
    Posts
    177
    Quote Originally Posted by slb8101 View Post
    The twenty degree rule is for the varable speed machines, normally 72-78 degree tower water with a fixed setpoint you should not have a surging problem. Iwould be looking at the cleanliness of the tubes both cooler and condenser, refrigerant charge,linear float metering device. possibly air in the machine from the factory i saw a few of those machines slip out of the factory with non condensibles still left in the system.
    Iwould also check water flows across both barrells to see if they are within design criteria and any head pressure control valves or tower bypass valves. I hope this helps as for the 10 -10 -10 rule I do not know.

  13. #13
    Sorry I thought the 10 10 10 rule of thumb was universal in a way. Here's what the 10 10 10 rule is by example:

    It's basically your approach

    cooler approach is 10* : SST 35* H2O OUT 45* H20 IN 55* = DELTA T OF 10* SO THE 10 10 10 RULE IN AFFECT
    condensor approach is 10*: SCT 95* H2O OUT 85* H20 IN 75* = DELTA T OF 10* SO THE 10 10 10 RULE IN AFFECT
    lift from the SST - SCT : SST 35* - SCT 95* = 60* DELTA T OF 60*

    So a surge is a momentary reversal of flow due to exceeding your lift.
    plus whats your cooler, condensor, and tower approach because that will tell you alot about what's going on to right ?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event