    York Surge Protection

    I apologize to anyone reading this in the refrigeration forum - obviously my mistake.
    Is there any way to provide surge protection for a York chiller using the keyless panel. Does the latest eprom contain algorithyms for this protection or is there some type of generic control that can be added to the panel. Thanks for all replies.

  2. #2
    Join Date
    Nov 2006
    Location
    US
    Posts
    112

    Question

    I think you need to be more specific, surges are only a by product of machine running out of design, is it a speed drive machine, what is your chilled water setpoint, what is your condenser water setpoint

  3. #3
    Join Date
    Oct 2007
    Location
    california
    Posts
    57
    Is unit a Optiview/Optispeed unit? If so it will map itself and lock out the chiller from running in that condition again in the future unless someone cleared mapping.

  4. #4
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    407
    Sorry guys, would have thought the "keyless micro" would have distinguished this panel from the optiview panel. It is a single speed compressor, was looking to see if any yorkies know of an eprom upgrade for the keyless panel that provides the same amount of surge protection that is available with the optiview panel. Current eprom number is 031 01431 002

  5. #5
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    No such EEPROM is available for a fixed speed chiller.
    The newer VSD's with Optiview has a seperate board(ACC Board)that looks for surges & logs them in memory...The required inputs and memory far exceed the capability of any known EEPROM.
    Ain't "None" of us as smart as "All" of us..

  6. #6
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    407
    Thanks for the reply Richard....... its what I suspected

  7. #7
    Join Date
    Nov 2006
    Location
    US
    Posts
    112
    I say sell them a vsd retrofit, by the way why is it surgeing does it have high tower water temp or low load or??????

  8. #8
    Join Date
    Nov 2006
    Location
    US
    Posts
    112
    I say sell them a vsd retrofit, by the way why is it surgeing does it have high tower water temp or low load or??????

  9. #9
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    407
    Quote Originally Posted by 9675 View Post
    I say sell them a vsd retrofit, by the way why is it surgeing does it have high tower water temp or low load or??????
    Combination of both at various times. Customer insists on running 38F water and has had tower issues over the summer at various times.

  10. #10
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by hw chiller man View Post
    Customer insists on running 38F water

    why does he need it that cold?



    .

  11. #11
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    407
    Quote Originally Posted by Airmechanical View Post
    why does he need it that cold?



    .
    This is an automobile assembly plant. The customer has many issues with how the water is used in his process. All of these issues would require his personnel to repair. It is much easier on his part to say "colder water" than to repair or redesign his proceses.