The efficiency loss is due to the thermal transfer of heat through the metal heat exchanger. When a heat exchanger is designed to transfer 95% of the heat produced through a certain amount of heat exchanger wall area at a certain temperature, then reducing the amount of Btu's of heat in that same space simply will not transfer the same percentage of heat through the walls of the heat exchanger. However; this reduction in heat transfer under properly operating conditions is no where near as low as Jim is inferring.
Single staged furnaces would simply short cycle more often which also decreases the rated efficiency of the furnace. Furnace efficiencies are rated at their peak performance in test labs under ideal conditions. Since all furnaces are rated this way, all furnaces are rated fairly. This does not mean that your furnace is going to always operate at peak efficiency in your home. Efficiency ratings is just a number determined during optimum conditions. When was the last time a vehicle you owned got anywhere near the gas mileage claimed by the manufacturer?
The Rheem/Ruud modulating furnace has been my personal favorite furnace for years. Now that other brands have come out with modulating furnaces, I may have other favorites to choose from. As with all staged furnaces, the Rheem modulating furnace is designed to operate as long as possible under the least amount of required heat to do the job keeping the home comfortable.
Because staged furnaces operate longer cycles, they do not waste fuel during as many warm up periods. All furnaces are very inneficient during the initial warm up of the heat exchanger. By keeping the heat exchanger warm longer, staged furnaces make up the difference in efficiency loss from low fire by not having to continually warm up the heat exchanger over and over again.
So, while low fire on staged furnaces may by itself be tested to be less efficient (50% is an extreme where something other then the furnace design was at fault), the efficiency loss on a properly sized furnace is still no greater then the efficiency loss on a single stage furnace cycling more often.
You guys really need to stop letting the Captain of Doom and Gloom scare you
Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
10-06-2008, 11:35 AM #71
Oh for crying out loud; let go of the Captain's 50% scare tactics! If all you are doing is looking for reasons to sue, then get Captain CO to go to court with you. Your furnace has been rated to a specific efficiency and under the conditions of the ratings it will perform those efficiencies. Since all furnaces are rated under the same regulations, your furnace is exactly what the manufacturer claims it to be under the conditions of the rating testing.
Yes! Jim is not lying. I have the utmost respect for Jim's knowledge and abilities. However, that guy on those Ginsu commercials is also not lying when he slices through rotten tomatoes and whipped cream with that knife that you haven't got a shot of being as good with when you get it home.Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
10-06-2008, 06:01 PM #72
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
Ok thanks for being helpful. Dang Some guys act like combustion science is some arcane art that you need to join a secret society to learn.
Well its good to know that I probably got a pretty hadle on the fundamentals so if I sign up for a course it won't be so tough for an older guy.
-
10-06-2008, 06:46 PM #73
LOL...
I know. Its strange how they will tell you how to check and adjust the charge of an A/C or HP, but ask about combustion. And its clam up time.
I can understand they might feel loyalty to Jim, and want him to make money.
But, then you would think they would not answer questions about anything else either, since there are schools and seminars for everything else also.
Some day, I may join that secret society. LOLLast edited by beenthere; 10-06-2008 at 08:19 PM.
-
10-06-2008, 07:53 PM #74
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
A member of my RSES chapter has subed for Jim davis (or so he says. I guess they are friends) and I know that guy is a combustion expert.
But we seem to have a controversy going now ,that caveman guy or what ever his name is, thinks he got boned and I think a lot of guys are starting to wonder what really is true or hype.
-
10-06-2008, 07:56 PM #75
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
And a joint would be good about now (check the spelling in the las line of your reply
).
-
10-06-2008, 08:19 PM #76
There is a slight drop in steady state combustion efficiency in first stage.
A CA can only tell you combustion efficiency, not total heat transfer efficiency.
Total heat transfer efficiency is effected by everything hooked to the system that effects air flow. Including return air temp.
A furnace is more efficient with a return air temp of 50°F, then it is with a return air temp of 85°F.
I tore out a 90% single stage, and installed a York 95% mod. It uses less gas for the year then the single stage did(which did supprise me).
It does seem to use a little more on some of the milder months(but the daughter was
home from college those months).
Other then when it was commisioned, its never been at full modulation(we're having warm winters for the last 3 years now).
And the gas usage is being compared to the first warm winter, which was the last winter the single stage was used.
I don't think the question should be how efficienct is a 90% furnace, But more, how efficient will the install situation/set up allow it to be.
A 80% with proper duct and register throw will use less gas the a 90% riding the high limit because of undersized duct work.
-
10-06-2008, 08:20 PM #77
-
10-06-2008, 08:52 PM #78
Regular Guest
- Join Date
- Apr 2008
- Location
- Upstate New York
- Posts
- 636
beenthere, I tapped EVERY joint on my duct work both hot and cold with metal duct tape. They are in my basement so maybe it didnt need to be done but it shouldn't do any harm right ? I was only going to do the cold air so it didnt suck any air from the basement but I did the hot also.
These ducts seem big, house built in 1955 all galv metal duct . Thx again for the help and the Valium