    Will my install be correct?

    Customer is adding 4 feet to his WI cooler.I have done my calculations and here is what I came up with.
    • new box size:6.5x12x7-approx 80sf-average use-btuh load with quick selection guide=6954 btuh
    • condensing unit(new)25f sst-7180 btuh
    • evap(used)6270@10td-9405@15td
    I figure with this new condensing unit and existing evap,I will have a 36f box @ 25f sst-with about a 11td.Does this sound correct or am I out to lunch?