Page 3 of 3 FirstFirst 123
Results 27 to 34 of 34
  1. #27
    Quote Originally Posted by badtech View Post
    to jayguy I can only get into 3 menus on this system
    i posted this last night but it seems to have disappeared so here it is again...more or less.
    0F is the lowest setpoint you can have.
    Trane has 6 menus in the controller. the other 2 menus are "hidden" and you need the password to access it. Trane hid it really well...in the IOM on page 93...duh!
    i think that you may have some inaccurate sensors (sat evap temp and/or comp temp sensor), so i would check them against a well known thermocouple. but like i said earlier, get those values and get your glycol levels up.
    running codes...
    74: Run Normal
    7E: Run Unload
    77: Run Evap Limit
    the chiller will run to maintain the load until the "saturated evap temp" hits the number programmed into menu #41. it will then unload (code 77) to maintain the "saturated evap temp" above its minimum setpoint (menu #41). at this point you will start losing your load.
    good luck.
  2. #28
    ottawa canada
    Six menus ???? you must be thinking about the chinese take away down the street (LOL) theres only five that I know of ??? Graham
  3. #29
    Delaware
    There are six (6) menu's but it can be argued that there ony 5. They are:
    Operating Display - Menu #0
    Service #1 Display - Menu #1
    Service #2 Display - Menu #2
    Auxillary Options Display - Menu #3
    Factory Display - Menu #4
    Factory Display - Menu #5
  4. #30
    Quote Originally Posted by graham View Post
    Six menus ???? ...
    menu P0.
    must be computer guys who came up with menus that start at 0!
    good luck.
  5. #31
    ottawa canada
    i
  6. #32
    ottawa canada
    Okay. Okay There are Five Menus in which control setpoints and parameters may be selected or adjusted ... is that better ?????? I hate computer geeks ??????? not you jay .
  7. #33
    ...I hate computer geeks ??????? not you jay .
    dittos to you too!
    good luck.
  8. #34
    Oct 2008
    Indiana
    sorry
    Hey guys I have not forgotten about you. I have been busy working on other stuff around campus. All of your guys input is great. I found that two of my pump drives in the building were put in bypass. Can you believe that crap. I found one too be working good and the other had a bad dc buss fuse on order now. graham, your help was tremendous. I have gotten with the local trane tech guy and have a nice binder on service bulletins for the Rtaa chillers. I will not go this long on checking in again! thanks to everyone badtech Oh hell I have been working on a Pool Pak and Carrier chiller. JUnk!