    Sounds like a lot of RTAA experience out there (good units) so I may as well jump into the mix. I beleive you just weighed in a new Ref charge? What about the oil charge? There is a method (in the IOM as I recall) of checking the oil level. It may be worth a shot. As mentioned, do not try to compare the RTAA and RTAC service wise as they are different designs and and do many things differently. Other things to look at are long periods of low load operation, low temperature operation, use of glycol ( as mentioned). Are you having load/unload problems or just low oil problems?

  2. #15
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,817

    Confused jay

    Quote Originally Posted by jayguy View Post
    sounds like you are doing some homework...good job.

    the displayed value in menu #27 is %RLA.

    do you have glycol in the system? if yes, what type and how much?

    what are these menu settings?
    1. 40
    2. 41
    3. 49
    4. 4A
    5. 4B
    6. 52

    also keep in mind that all pressures are converted from temp sensors

    good luck.
    jay,

    could this be from the broken 3/8 copper line inside the separator?
    i forgot the symptoms.

    st65
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  3. #16
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,853
    There is no 3/8 line inside the oil separator so I somehow doubt it could be broken . IOM3 page 83 shows a cutaway drawing of the separator and how it works . The discharge gas enters the separator at the top of the u tube but the entry points are offset to the tube so the gas swirls around causing the oil to separate .

  4. #17
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,011
    Quote Originally Posted by supertek65 View Post
    jay,

    could this be from the broken 3/8 copper line inside the separator?
    i forgot the symptoms.

    st65
    1. 40: Leaving Water Temp. Cutout Setpoint
    2. 41: Low Refrigerant Temp. Cutout Setpoint
    3. 49: Superheat Setpoint
    4. 4A: EXV Control Response Setpoint
    5. 4B: LWT Control Response Setpoint
    6. 52: Low Water Temperature EXV Gain Compensation

    i do not know about any 3/8 line. the above setpoints may point to an issue. i have a feeling that the "saturated evap temp" and compressor suction temp" sensors may be inaccurate but i wanted to know how the above items were set.

    good luck.
    It's tube brushing season...93% done (39.35 miles of tubing)...only 1,242 tubes to go!

    Original member of the Raccoon Brotherhood.

    EVERYTHING IS AWESOME!!!

  5. #18
    Join Date
    Oct 2008
    Location
    Indiana
    Posts
    10
    Hey guys. I think I have my oil nuisance problem fixed. The unloader valve had a dirty pill filter. I took it out and discarded it. Last time I checked when it started it was around 46%. It never tripped on oil flow after I did that. Now my low suction happens after the unit loads up. The system is very low on glycol. The technician that tested it said it was only 27 degrees. Past the EXV it frosts into the evap but, It is not frosted going to comp. I believe I have an RTAC next to this one and the digital display is showing a 44 suction it shows running normal. Could low glycol cause a low suction since the heat transfer is not as great with just water? Oh by the way we run our chilled water systems at 0 to minus 11. also unit shows 74 then 77 and after the unit runs then it goes back to 74 until unit goes into 7e then shuts down.

  6. #19
    Join Date
    Oct 2008
    Location
    Indiana
    Posts
    10
    to jayguy I can only get into 3 menus on this system

  7. #20
    Join Date
    Oct 2008
    Location
    Indiana
    Posts
    10
    hey g unit where can I find these service bulletins online at?

  8. #21
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    284
    You run the chiller at 0 to -11 degrees F with solution good down to 27 degrees? Am I reading this right? I would assume setpoint is Celsius because chiller setpoint I think only goes down to 0 F?
    Last edited by jimbob73; 10-06-2008 at 11:17 PM. Reason: spelling
    It's All Good!!!

  9. #22
    Join Date
    Jun 2006
    Location
    Midwest
    Posts
    284
    At setpoint of 0 to -11 C = 32 to 12.2 F, Your short on freeze protection/glycol. While there may be burst protection with flow, Solution would turn to slush which would cause pump efficiency/flow to drop and cause problems within the evaporator.
    It's All Good!!!

  10. #23
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,817

    heat transfer

    Quote Originally Posted by badtech View Post
    Hey guys. I think I have my oil nuisance problem fixed. The unloader valve had a dirty pill filter. I took it out and discarded it. Last time I checked when it started it was around 46%. It never tripped on oil flow after I did that. Now my low suction happens after the unit loads up. The system is very low on glycol. The technician that tested it said it was only 27 degrees. Past the EXV it frosts into the evap but, It is not frosted going to comp. I believe I have an RTAC next to this one and the digital display is showing a 44 suction it shows running normal. Could low glycol cause a low suction since the heat transfer is not as great with just water? Oh by the way we run our chilled water systems at 0 to minus 11. also unit shows 74 then 77 and after the unit runs then it goes back to 74 until unit goes into 7e then shuts down.
    i believe heat transfer is better or more thermal conductivity with water
    than with glycol, you lose btus with glycol
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  11. #24
    Join Date
    Sep 2008
    Location
    Delaware
    Posts
    243
    The best heat transfer is acheived using water alone. When you add glycol the heat transfer starts to get worse and the unit has to work harder to pull out the same amount of heat. Thus the reduction in capacity. The more glycol, the less capacity. There are capacity correction charts for that machine (and others) when using glycol.
    There are no parts,tubes, or anything inside the oil seperator. Just a big, ugly, round "U" tube for oil seperation by centrifugal force (as mentioned earlier).

  12. #25
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,853
    Ok well done on finding the dirty pill filter . did you check the amperage at start up ??
    At this point I really think you need to get hold of not only the service bulletins I gave you numbers for but also the main IOM IOM 3 it is a very informative manual and explains how to access all five menus and all the settings for each men . It also shows diagrams and cut away drawings for compressors and oil circuit etc.
    One setting to check is in menu 4 for LWT below 38degrees you have to enable the EXV low solution temp gain compensation to properly control the EXV at low LWT"S. This may be your issue ??
    All the info is available from your local Trane Office (or possibly Jayguy if you ask nicely) Im not computer savvy enough to know how to send them to you .
    also check the chart in the IOM that explains what the ideal settings are for the menu 4 items that Jayguy mentioned ,they are critical and so is the recommended glycol concentration .
    good luck Graham

  13. #26
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,853
    I made a mistake about the EXV compensation setting its in menu 5 and its for LWT settings below 40degrees f . It has to be set to enable .. sorry for the confusion . graham

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event