i posted this last night but it seems to have disappeared so here it is again...more or less.
0F is the lowest setpoint you can have.
Trane has 6 menus in the controller. the other 2 menus are "hidden" and you need the password to access it. Trane hid it really well...in the IOM on page 93...duh!
i think that you may have some inaccurate sensors (sat evap temp and/or comp temp sensor), so i would check them against a well known thermocouple. but like i said earlier, get those values and get your glycol levels up.
running codes...
74: Run Normal
7E: Run Unload
77: Run Evap Limit
the chiller will run to maintain the load until the "saturated evap temp" hits the number programmed into menu #41. it will then unload (code 77) to maintain the "saturated evap temp" above its minimum setpoint (menu #41). at this point you will start losing your load.
good luck.Time to get my nerd on!
-
10-08-2008, 05:03 PM #28
Six menus ???? you must be thinking about the chinese take away down the street (LOL) theres only five that I know of ??? Graham
-
10-08-2008, 05:20 PM #29
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
There are six (6) menu's but it can be argued that there ony 5. They are:
Operating Display - Menu #0
Service #1 Display - Menu #1
Service #2 Display - Menu #2
Auxillary Options Display - Menu #3
Factory Display - Menu #4
Factory Display - Menu #5
-
10-08-2008, 06:06 PM #30
-
10-08-2008, 06:29 PM #31
i
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
10-08-2008, 06:30 PM #32
Okay. Okay There are Five Menus in which control setpoints and parameters may be selected or adjusted ... is that better ?????? I hate computer geeks ??????? not you jay .
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
10-08-2008, 09:37 PM #33
-
10-22-2008, 09:58 PM #34
Regular Guest
- Join Date
- Oct 2008
- Location
- Indiana
- Posts
- 10
sorry
Hey guys I have not forgotten about you. I have been busy working on other stuff around campus. All of your guys input is great. I found that two of my pump drives in the building were put in bypass. Can you believe that crap. I found one too be working good and the other had a bad dc buss fuse on order now. graham, your help was tremendous. I have gotten with the local trane tech guy and have a nice binder on service bulletins for the Rtaa chillers. I will not go this long on checking in again! thanks to everyone badtech Oh hell I have been working on a Pool Pak and Carrier chiller. JUnk!