    i have this client who has a 600 sq ft house with a 750000 btus copper fin boiler combined with a 15 ton air cooled Trane chiller (CGA series). There 22 radiators with blowers and drain pans throughout the house. Every year i have to winterize this chiller by purging the heat exchanger with nitrogen. So every year i remove the water in the chiller piping and
    HX and i refill the system the next summer when i shut off the boiler... I want to relocate the HX inside the building (appprox 20 ft of refrigerant piping) near the boiler . Can it cause a problem?? is it better to go with glycol.? Temps in winter can be as low as -40 F
    Learn as if you were to live together and live as if you were to die tomorrow. -Gandhi

  2. #2
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    I wouldn't relocate it. What's the big deal with draining it every year? Easy money if you ask me. We do it on commercial units all the time adding glycol is fine but if it shares a common loop with your b oiler system the concentration you will need to provide adequate freeze protection will reduce your boiler efficiency quite a bit. Good luck.

  3. #3
    Join Date
    Oct 2001
    Posts
    6,962
    Post Likes
    the chiller has power up during the winter for the CCHs...how about wrapping the barrel with some low resistance heat tape like they do on towers lines that run in the winter.the nitro is doing the job as long as you do the drain plugs on the lowest point of the lines just outside the chiller.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  4. #4
    Join Date
    Mar 2008
    Location
    Montreal
    Posts
    106
    Post Likes
    Thread Starter
    Quote Originally Posted by mustardman View Post
    I wouldn't relocate it. What's the big deal with draining it every year? Easy money if you ask me. We do it on commercial units all the time adding glycol is fine but if it shares a common loop with your b oiler system the concentration you will need to provide adequate freeze protection will reduce your boiler efficiency quite a bit. Good luck.
    do you think changing the water can damage black iron pipes of my system
    ?
    Learn as if you were to live together and live as if you were to die tomorrow. -Gandhi

  5. #5
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,116
    Post Likes
    [QUOTE=refmet;2006143]do you think changing the water can damage black iron pipes of my system
    ?[/QUOTe

    Yes in a sense when you drain a system down you have air in a likely partially wet system so it can corrode your pipes quicker. However stagnent water with no chemical treatment is a problem too. I am no water treatment expert by any stretch but to me draining your system and adding a chemical program at start up is the way to go.

  6. #6
    Join Date
    Nov 2007
    Posts
    376
    Post Likes
    Quote Originally Posted by refmet View Post
    I want to relocate the HX inside the building (appprox 20 ft of refrigerant piping) near the boiler . Can it cause a problem??
    It is very poor practice, it may be a code violation, to put refrigeration equipment in a room that also contains fuel burning appliances, unless the appliance has sealed combustion or you interlock the boiler's operation with a refrigerant monitoring panel. Refer to ASHRAE Standard 15 for more detailed info.

  7. #7
    Join Date
    Oct 2004
    Location
    Metro ATL
    Posts
    459
    Post Likes
    The problem I see in a remote location would be refrigerant migration with no water flow causing the evap to freeze.

  8. #8
    Join Date
    Mar 2008
    Location
    Montreal
    Posts
    106
    Post Likes
    Thread Starter
    Quote Originally Posted by jemawalton View Post
    The problem I see in a remote location would be refrigerant migration with no water flow causing the evap to freeze.
    with no water flow?? I have only one pump and it is always on in order for the zoning system to work...can you elaborate pls
    Learn as if you were to live together and live as if you were to die tomorrow. -Gandhi

  9. #9
    Join Date
    Mar 2008
    Posts
    71
    Post Likes
    Quote Originally Posted by jemawalton View Post
    The problem I see in a remote location would be refrigerant migration with no water flow causing the evap to freeze.
    Ive only heard of this happening on Trane RTAC's. Something to do with the falling film evap. I dont totally buy the refrigerant migration theory the factory gives.