    TXV question

    I am trying to diagnose a problem with an R-22 system that was just retrofitted to R-410a after a major compressor burn out. The system has a 4 ton evap coil and 3 ton TXV and condensing unit. The system was flushed of contaminants, piston orifice removed, condensing unit replaced, suction and liquid dryers installed, and TXV added. After the retrofit/repair was complete I started the system and it ran at normal pressures for a good amount of time. After a few minutes, the suction pressure stood still, but the head pressure climbed and climbed and climbed, until it was up to about 575 to 600 psig. At this point I pulled the disconnect, waited, and tried again. Same deal. I have a few ideas but I'm trying to get some other opinions before I have to go back to the job tomorrow. I figured there was a restriction or a jammed shut TXV, but in that situation I would expect to see the system pumping down the low side but it didn't. The low side stays at about 140 psig but the high side just keeps going up. So, I'm lost for now. Contaminated system? Bad TXV? Sensinb bulb location? Help would be greatly appreciated. Thanks.

  2. #2
    Join Date
    Jun 2007
    Location
    south carolina
    Posts
    175
    need to go to pros forum for that.

  3. #3
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,701
    Did you happen to check thetemp drop across your liquidline drier?Stop the indoor fan for an equal frost pattern? How long does it take until the pressures sky rocket? There`s a few to start.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  4. #4
    Join Date
    Jun 2008
    Location
    va
    Posts
    800
    R22 TXV?

  5. #5
    probalby overcharged. you need to take subcooling and superheat readings for a good diagnosis.

    best thing to do is take a clean recovery drum and dump most of the refigerant into it. then charge unit untill proper subcooling is obtained. then check superheat. If superheat is low then check for low air flow if superheat is high then check txv, driers and of course if superheat is good then your ok.

  6. #6
    Join Date
    Apr 2004
    Location
    Charlotte, NC
    Posts
    648
    Could be a condenser fan motor failing, but I would tend to lean towards a failing headmaster.
    "Fighting Ignorance since 1973 (It’s taking longer than we thought)." The Straight Dope.

  7. #7
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,705
    you hooked up a new 410 unit to an old 22 coil and it don't work????

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,722
    Are you using the old R22 evap coil.

    Brand and model numbers of both indoor coil/air handler, and outdoor unit would help.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    lol

    i hope he meant changed out a 22 "system" with a 410a "system"

    rotf
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  10. #10
    Join Date
    Oct 2008
    Location
    Central New York
    Posts
    4
    Yes, it is a 4 ton R-22 coil inside of a Carrier fan coil unit with a 3 ton Bryant Evolution condensing unit. 3 ton 410a TXV. Model and serial numbers are not handy right now. If I remember correctly the condensing unit is a 187ANA. If I had it my way this job would have not been done this way, but I was not the one who set it up, but was the one who got stuck doing it. I appreciate the help, I'll try out these suggestions tomorrow and see what I come up with. Thanks.

  11. #11
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    is it a heat pump? if so run the heat and see what happens

    other than that, you need some pro help and this is not pro section
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event