    401B

    Could you share your knowledge and experiences with 401B. I recently came across a compressor with a tag that it had been changed to 401B. I have no experience with this refrigerant. At what applications is it best used?

  2. #2
    Join Date
    Jul 2007
    Location
    regina saskatchewan
    Posts
    257
    Artificial Intelligence is no match for Natural Stupidity

  3. #3
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,265
    Quote Originally Posted by kerreckt View Post
    Could you share your knowledge and experiences with 401B. I recently came across a compressor with a tag that it had been changed to 401B. I have no experience with this refrigerant. At what applications is it best used?
    R401B is primary intended as an interim service replacement refrigerant for low temperature R12 systems.

    Since no R12 freezers have been made since about 1993, the likelihood of needing it becomes less every day. With the high cost of this refrigerant today, it's not likely you'll go running out to buy 30 lbs to charge up a 2 lb system that may well be the last R12 LT system you'll ever see.

  4. #4
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    good sweet juice never had any problem with it
    again what application ? you cannot use for ice cream
    -15* evap

  5. #5
    Join Date
    May 2008
    Location
    S.E.Virginia
    Posts
    87
    I was thinking of using it for a walk in freezer.

  6. #6
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    Quote Originally Posted by kerreckt View Post
    I was thinking of using it for a walk in freezer.
    what kind REF do you have before ?

  7. #7
    Join Date
    May 2008
    Location
    S.E.Virginia
    Posts
    87
    I will be putting a new condensing unit on a box that had R502 in it until it died.

  8. #8
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    486
    Quote Originally Posted by kerreckt View Post
    I will be putting a new condensing unit on a box that had R502 in it until it died.
    Go with R404a if you are changing the condensing unit. It will work fine w a 502 evap. You won't even have to change the txv, just make sure to get all the mineral oil out before you switch to the POE oil.

  9. #9
    Join Date
    May 2008
    Location
    S.E.Virginia
    Posts
    87
    I usually use 404a. I had seen 401b used and thought there might be some compelling advantage......thanks

  10. #10
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    Quote Originally Posted by kerreckt View Post
    I usually use 404a. I had seen 401b used and thought there might be some compelling advantage......thanks
    R-404a should be your choice