Results 1 to 10 of 10
Thread: 401B
    May 2008
    S.E.Virginia
    401B
    Could you share your knowledge and experiences with 401B. I recently came across a compressor with a tag that it had been changed to 401B. I have no experience with this refrigerant. At what applications is it best used?
    regina saskatchewan
    Artificial Intelligence is no match for Natural Stupidity
    Jul 2000
    Guayaquil, EC
    Quote Originally Posted by kerreckt View Post
    R401B is primary intended as an interim service replacement refrigerant for low temperature R12 systems.
    Since no R12 freezers have been made since about 1993, the likelihood of needing it becomes less every day. With the high cost of this refrigerant today, it's not likely you'll go running out to buy 30 lbs to charge up a 2 lb system that may well be the last R12 LT system you'll ever see.
    Nov 2005
    Haymarket VA
    good sweet juice never had any problem with it
    again what application ? you cannot use for ice cream
    -15* evap
    May 2008
    S.E.Virginia
    I was thinking of using it for a walk in freezer.
    Nov 2005
    Haymarket VA
    what kind REF do you have before ?
    May 2008
    S.E.Virginia
    I will be putting a new condensing unit on a box that had R502 in it until it died.
    Cedar Rapids, IA
    Go with R404a if you are changing the condensing unit. It will work fine w a 502 evap. You won't even have to change the txv, just make sure to get all the mineral oil out before you switch to the POE oil.
    May 2008
    S.E.Virginia
    I usually use 404a. I had seen 401b used and thought there might be some compelling advantage......thanks
    Nov 2005
    Haymarket VA
    R-404a should be your choice