    True Meltdown

    I got a call from a meat market customer Thursday at 5:30 AM shortly after the deli kitchen crew came in. They said the store had a burning smokey odor and the 3-door reach-in freezer was making loud popping sounds and flashes of light.

    Fortunately, they managed to find the breaker for that case and shut it down. I arrived a while later to find this:


    Note the melted temperature control knob:


    Lot's of smoke staining too. (Yes, that's one of my TEV conversions):


    The product on the lower four shelves was still hard frozen. The stuff on the top shelf was not only thawed, but actually cooked.

    Can't figure out what the heck this fuzzy crap is on the doors:


    Got the coil plenum down to see what was going on up there. Note the insulation dripping from that brown wire:


    Then I found the source of the terribly acrid smoke. The melted wiring had shorted to the evap coil blowing several pounds of R404A and a bunch of POE oil into a glowing maze of defrost heater elements. It's hard to see, but there's a hole in the top front return bend.:


    Of course all this fried wiring goes up into the box insulation in the top and ends up down at the right front bottom of the box. No repairing that.

    How did this happen? This case had no defrost limit thermostat. I'm still not sure how it all started, but it certainly wouldn't have gotten this far if the case were designed to have a safety limiter for the heaters. (It has one for the door frame heaters but not the defrost heaters....go figure)

  2. #2
    crackertech's Avatar
    crackertech is offline Educational Committee/Professional Member*
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,501
    Quote Originally Posted by icemeister View Post

    Of course all this fried wiring goes up into the box insulation in the top and ends up down at the right front bottom of the box. No repairing that.
    Oh come on now that should be a quick repair nothing to really.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  3. #3
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,410
    One of those wires short out on the u-bend?

    I’ll bet the solenoid coil on the clock is swelled!

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,259
    Quote Originally Posted by pecmsg View Post
    One of those wires short out on the u-bend?

    I’ll bet the solenoid coil on the clock is swelled!
    Yes, a wire shorted to the return bend. You can see it best in the next to the last pic...that spot on the copper is melted insulation, the burn hole is at the top of that.

    The solenoid coil looked OK but even if the termination failed the failsafe was set at 30 minutes should have de-energized the defrost heaters.

    The contacts on the timer were pretty well pitted and burnt. I'm theorizing that the #3 contacts were welded together but broke apart after things cooled down.

    In any event, I'm adding a defrost limit thermostat so this won't happen again.

    I wonder how this design ever passed UL?

  5. #5
    Join Date
    Sep 2008
    Location
    Morehead City, NC
    Posts
    29
    That just completely blows my mind... I can't wait to start posting my pictures on here...
    "The truth only hurts when it should"

  6. #6
    Join Date
    Jul 2008
    Posts
    100
    Hey Ice,

    There should have been a delay and a limit in that case, I confirmed it with Ron T yesterday.

    He did mention that two models of the newer GDM and T series do not have the delay.

    Do you have a model and serial of the case?

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,259

    Coldcube, Here you go...

    M/N GDM72F
    S/N 1-1497739

    Here's a pic of the wiring schematic. No limit for the defrost heaters, just the door heaters:


  8. #8
    Join Date
    Jul 2004
    Location
    NJ
    Posts
    1,793
    I can't agree more about the limiting thermostat,I have been adding them whenever I come accross a freezer that doesn't have them.I also never ever cancel DTTs.Learned it the hard and scary way a couple of years ago at a BP gas station store.
    Hopefully it can be noticed that there is a defrost termination problem when there is a limiting thermostat though..Before it fails in the CLOSED position.

  9. #9
    Join Date
    Mar 2006
    Location
    south jersey
    Posts
    454
    Well at least they didn't use a Hydrocarbon refrigerant or it could have been much worse.
    Would the last person to leave NJ please put out the lights

  10. #10
    Join Date
    Jul 2008
    Posts
    100
    I followed up with Ron T today.

    The case is from 1996. At that time a termination/delay was all that was required for "safe operation". Just on a side note, any changes to the case, including the addition of an expansion valve and receiver will void warranties and the UL stamp.

    Before I get barbequed, I personally understand the benefit of the expansion valve.

  11. #11
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,259
    Quote Originally Posted by coldcube View Post
    I followed up with Ron T today.

    The case is from 1996. At that time a termination/delay was all that was required for "safe operation". Just on a side note, any changes to the case, including the addition of an expansion valve and receiver will void warranties and the UL stamp.
    ...As would the addition of a defrost limit safety thermostat.

    Quote Originally Posted by coldcube View Post
    Before I get barbecued, I personally understand the benefit of the expansion valve.
    ...And that defrost limit will hopefully prevent this box from another barbecue.

    Interestingly, I spoke with a claims agent from Hartford Steam Boiler Insurance yesterday and he considered the defrost limiter would be an excellent add.

  12. #12
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,518
    Quote Originally Posted by coldcube View Post
    I followed up with Ron T today.

    The case is from 1996. At that time a termination/delay was all that was required for "safe operation". Just on a side note, any changes to the case, including the addition of an expansion valve and receiver will void warranties and the UL stamp.

    Before I get barbequed, I personally understand the benefit of the expansion valve.
    Tru-apper must have not liked the way ice did it because you can get TXV's installed at the factory for a remote box and what's wrong with remoteing it underneath

    I had a W/I melt down where sparky connected 208 V to H1 and H2 on a Friday afternoon

    All the plastic cam plugs melted out

    Fan guards looked like the toxic avenger

    No recognisable wiring and motors fried

    And of course they wanted it fixed




    This R/I had a paper top and I believe they use metal now





    It probably would have burned out but somebody opened the doors and popped the top

    You can kind of see the metal motors where they melted and pooled up metal puddles like in Terminator
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  13. #13
    Join Date
    Mar 2005
    Posts
    664
    Must have been a real chinese firedrill in that kitchen when that was goin on! best to replace box? i would!! good luck stan
    Keep it simple to keep it cool!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event