Results 1 to 9 of 9
    Phoenix,AZ
    Adjusting SH on multi evaps?
    Got a call to a big walk-in beer cooler not holding temp (45°F). Looked at copeland semi-hermetic first. Head frosted and discharge line luke warm. (floodback)
    Each evap had its own LLSV and T-stat. So i shut off one evap and adjusted TXV for 8 degrees SH on running one and then i shut off that one and adjusted other for 8 degress SH. Is this how you guys would approach this sitiuation or would you adjust them while both of them were running?
    Southold, NY
    It’s difficult to check superheat on a 5,000btu evaporator with 10,000btu’s of compressor. I recommend adjusting while both are running with the box near operating range.
    I have run into a similiar situation before.
    The two evaporator coils being in the same box or area should be controlled by one thermostat controling both liquid line solenoid valves.
    It will work much better that way.
    arlington, tx
    you always want to adjust at full load
    Nov 2005
    Haymarket VA
    Quote Originally Posted by kbghdg View Post
    just 14 * rule of thumb evap SH on high load then come back when its running on design temp set Sh good to go
    Phoenix,AZ
    Quote Originally Posted by mechanicalgsxr View Post
    Meaning what?
    I would think with one evap shut off and more refrigerant available and horsepower flowing to the other your greatest chance of floodback would then occur. Am i wrong?
    Meaning what?
    If you adjust the valves to the proper SH while at full load then they should throttle back and maintain that SH as the box temp drops and the load is reduced. As was mentioned in an earlier post, If both evaps are in the same box why not control both LLSV's with the same t-stat.
    Jun 2001
    Michigan
    if the condensing unit has no way to shed load, such as Hot Gas By Pass, or unloading, I would not run those evaporators individually rather run on one stat.
    A walk in such as this, there is no need to control each coil individually. It's all doing one load.
    And if the coils were doing two separate load spaces, then obviously individual control is needed, then we we have to modify condensing equipment to modulate capacity.
    arlington, tx
    Quote Originally Posted by jwc64 View Post
    what he said lol