Results 1 to 13 of 16
    Is the existing duct good for a new 4 ton ac
    Currently, we have 14" main flex duct and 8" flex duct for outlets. Measurements were taken from outside sides so probably the inside airflow diameters are little smaller. We are doing an addition and the ac contractor said that we need a 4 ton after doing computer calculations. He also said that the existing duct is not big enough. We are on a tight budget.
    Is the existing duct enough for a 4 ton ac?
    If your main duct is 14" that is not even close for a 4 ton. That is the reason your contractor told you it was not big enough.
    Is the 8" outlets ok. We have 10 and adding another 2.
    That part sounds ok.
    12 ,8" branch ducts may or may not be okay.Being they are all 5" ,it sounds like the duct system was not designed correctly,seldom if ever would all branch runs be the same size,as they are feeding different rooms/areas.
    What is the physical relationship between the indoor unit,existing home,and the adddition?how large is the addition?
    What size/tons is the old system?
    The existing house is around 1400-1500 square feet and the existing ac is 3 ton.
    The addition will add another 600-700 square feet.
    What would happen if I leave the duct work as is with the new 4.0 ton ac?
    It will be noisy, you risk freezing up of the coil, they may have to overcharge to get the low side pressure high enough to avoid freezing which is hard on the compressor. The efficiency takes a dive so you'll really get much lower than the 13 SEER or whatever you think you are getting, even though you went 33% larger, you may not gain a lot in cooling due to the low airflow.
    1)could void warranty
    2)poor performance
    3)greatly reduce equipment life
    I would not pay to increase size of equipment if you are not going to correct ductwork. I run into this all the time. I know times are tight but people love to do additions but always seem to want to cut corners on the HVAC. Then they have spent money on something that they are not even comfortable in. Then they complain about it forever.
    I will try to at least replace the main duct.
    Quote Originally Posted by GG123 View Post
    Ask if they can simply run an additional "trunk duct" from very near the indoor unit,out to the new branch ducts for the addition.
    Also new to provide a return duct or return path for the supply air to the addition.
    Will do
    NW burbs of Detroit
    Man you gotta love flex duct...it's more a victim of hacks then metal will ever be.....I feel the OPs pain