Lon interface submittals
Results 1 to 2 of 2
  1. #1
    Join Date
    Mar 2008
    Posts
    86

    Lon interface submittals

    I am doing drawing for a job that has a lon interface with a Trane rooftop unit (actually 2). How do you guy handle the interface on the drawings. Do I put the Sequence on the drawing as usual or just note that the manufacture is responsible for meeting the sequence and that I will provide GUI to all points delivered by manufacture? In the past I have done both, but could use a break from typing.

  2. #2
    Join Date
    May 2002
    Posts
    9,564
    Why not say it must meet Lonmark - or specify the variables/names you want to see at a minimum with overrides? Additionally, I'd require that if there are any undefined variables, that they must be clearly explained in documentation what they do.