    Over-sized valve?

    I have been wrestling with sizing this "chilled water valve" all day, This system will include 100% Outside Air, steam pre-heat,50%glycol, and reheat. Of course the chiller is oversized to allow for 95 degree outside air (85 tons). 12,000 cfm air handler (approx. 30 tons air). The existing pipe size is 4", and the system has approx. 35 ft of head. The submittals list the chilled water flow at 143.75 gpm. I have used every calculation in "the book" and I have determined that the valve should be sized @ 68 to 72 Cv. The problem is:

    #1 The existing pipe is 4"
    #2 The required (68 Cv) calls for a 2.5" valve @ 5 psi delta P
    #3 Cv for a 2.5" valve is 54Cv
    #4 Cv for a 3" valve is 83Cv
    #5 delta P is 7.7 psi for a 2.5" valve
    #6 delta P is 3.3 psi for a 3" valve
    #7 reducing from 4" to 2.5" may cause cavitation
    #8 using a 3" valve could mean oversized valve and loss of control (hunting)

    The submittal also list the pressure drop for the chilled water coil at 19 psi (seems excessive).

    What the "!%&*"

    Any help sizing this valve will be appreciated, need more information? I got it.

  2. #2
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    I am not a valve expert by any means but have you contacted a few valve manufacturers to see what they have to say? My thought is an "oversized" valve with a characterized disc to actually get the value you want/need.

    Or control it like steam 1/3 and 2/3! ;o)
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  3. #3
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    I would size it up for the 68cv, bumping up the to the next size valve if the 2.5" will not cover it. I would not hesitate to put a 3" with a cv of 83 as your 2" will not meet the 5# drop. However I always thought the control valve should have the bigger pressure drop vs the coil.

    It will only be oversized if you botch the selection.....


    When in doubt call the valve manufacture.

  4. #4
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Something is not right with your numbers.

    If the system only has 35ft of head your not going to be able to push water through that coil.

    35/2.31=~15psi

    That must be the fill pressure, not pump head?
    Last edited by orion242; 09-24-2008 at 02:45 AM.

  5. #5
    Join Date
    Mar 2008
    Location
    Baltimore
    Posts
    50
    Post Likes
    19 PSI seems excessive for the pressure drop through the coil. The valve needs to be sized to take a larger pressure drop than the coil. If the coil is taking a larger pressure drop than the valve, the coil becomes the "authority" in the system and modulating the valve at the high end of the stem travel will have no effect.

  6. #6
    Join Date
    May 2007
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by orion242 View Post
    Something is not right with your numbers.
    If the system only has 35ft of head your not going to be able to push water through that coil.
    35/2.31=~15psi

    That must be the fill pressure, not pump head?
    Your are correct, after checking the pump submittals, I found that the pump is designed at 75 TDH and 150 GPM.

    And yes I could call someone and have them size the valve for me, but then what would I (and others) learn from that? I have learned already that you must first have accurate information

    So here is the latest;

    Pump designed at 75 Ft/H2O
    Coil pressure drop = 19.27 Ft/H2O (not psi)
    designed coil flow = 143.75 GPM
    designed pressure drop for valve 5 PSI
    Chilled Water 42 degrees
    Existing Pipe Size entering valve = 4"
    50% ethylene glycol = 1.05 SG
    Did the Math and I come up with "65 Cv"

    My choices for a flanged valve are
    2 1/2" valve with 54 Cv 28 psi closeoff
    3" valve with 80 Cv 12 Psi closeoff

    Now the question would be which valve would be more suited for this application, and why

    Thanks

  7. #7
    Join Date
    Mar 2008
    Location
    Baltimore
    Posts
    50
    Post Likes
    I would select the 2-1/2 inch valve for two reasons:

    1. The pressure drop is about 7.5 psi which is below, but fairly close to the pressure drop of the coil (8.34 psi). This will yield a larger range of control than the 3 inch valve.

    2. The 3 inch valve may not be able to close off against the pump head and will tend to "chatter" when trying to control at the low end of the range during low load conditions.

  8. #8
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,780
    Post Likes
    Quote Originally Posted by nickolas View Post
    Your are correct, after checking the pump submittals, I found that the pump is designed at 75 TDH and 150 GPM.

    And yes I could call someone and have them size the valve for me, but then what would I (and others) learn from that? I have learned already that you must first have accurate information

    So here is the latest;

    Pump designed at 75 Ft/H2O
    Coil pressure drop = 19.27 Ft/H2O (not psi)
    designed coil flow = 143.75 GPM
    designed pressure drop for valve 5 PSI
    Chilled Water 42 degrees
    Existing Pipe Size entering valve = 4"
    50% ethylene glycol = 1.05 SG
    Did the Math and I come up with "65 Cv"

    My choices for a flanged valve are
    2 1/2" valve with 54 Cv 28 psi closeoff
    3" valve with 80 Cv 12 Psi closeoff

    Now the question would be which valve would be more suited for this application, and why

    Thanks
    Could you please show the complete process/calculations required to size the valve? Complete the lesson so to speak.
    Thanks,
    Jogas
    Four wheel therapy, my 1968 Camaro is gone and will be missed

  9. #9
    Join Date
    Feb 2005
    Posts
    345
    Post Likes
    One rule of thumb is a 3psi drop for the valve so your calc'd Cv is 82. This valve would be on the large size but if it's a ball valve with a characterized disk it'll control just fine. Sounds like your 3" choice @ Cv80 is the one you want (assuming it has a disk)

    Nikko

  10. #10
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    489
    Post Likes
    Quote Originally Posted by jdd67 View Post
    I would select the 2-1/2 inch valve for two reasons:

    1. The pressure drop is about 7.5 psi which is below, but fairly close to the pressure drop of the coil (8.34 psi). This will yield a larger range of control than the 3 inch valve.

    2. The 3 inch valve may not be able to close off against the pump head and will tend to "chatter" when trying to control at the low end of the range during low load conditions.
    If the chiller is designed for the ahu and solely for that purpose I would think you should have a 3 way valve to prevent cutting down the water flow to nothing. Why do you need to control the water flow if this is the only coil on the chiller? Can't you control the load by raising the setpoint of the water?

  11. #11
    Join Date
    May 2007
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by jogas View Post
    Could you please show the complete process/calculations required to size the valve? Complete the lesson so to speak.
    Thanks,

    Cv = Q √SG/ΔP

    Where
    Cv = Flow Coeffecient
    Q = Flow Rate in GPM
    sg = specific gravity
    ΔP = Wide open pressure drop (Psi)


    65.87 = 143.75 √1.05 / 5

  12. #12
    Join Date
    May 2007
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by bob_scheel View Post
    If the chiller is designed for the ahu and solely for that purpose I would think you should have a 3 way valve to prevent cutting down the water flow to nothing. Why do you need to control the water flow if this is the only coil on the chiller? Can't you control the load by raising the setpoint of the water?

    The chiller is designed for this AHU and coil only, I will be using a 3 way valve to maintain full flow to the chiller under all conditions. The specification requires 55 degree air leaving the chilled water coil, which will then be reheated if needed to maintain space temp, also the chilled water valve will be forced to 100% during the dehumidification cycle causing the reheat coil to maintain space temp.

    I have used this sequence before and it works well if controlled properly
    Last edited by nickolas; 09-24-2008 at 08:40 PM. Reason: additional comment

  13. #13
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    Caution! Make sure your valve has the flow characteristics that you need in for both the cooling coil and then when it is in full bypass. We recently had to change out 2 valves, and I don't know all the details as I was just told about it, due to the bypass position not allowing enough flow - anyway one chiller serving two air handlers.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  14. #14
    Join Date
    May 2007
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by crab master View Post
    Caution! Make sure your valve has the flow characteristics that you need in for both the cooling coil and then when it is in full bypass. We recently had to change out 2 valves, and I don't know all the details as I was just told about it, due to the bypass position not allowing enough flow - anyway one chiller serving two air handlers.
    Good point; For that reason maybe the " 3 " inch valve would be more suitable in this case. (to insure required flow to the chiller in bypass). I think I have all the infomation necessary to select the proper valve.

    One thing that I am sure of is, that the selection has not been "botched"

    "Orion242--It will only be oversized if you botch the selection....."

    Thanks guys I have learned a lot

  15. #15
    Join Date
    Jun 2007
    Posts
    175
    Post Likes
    I am in no way a valve expert, but have picked up a few things along the way. If the pipe is 4" and you do place a 3" or even 2 1/2" valve in line, I know the Cv must be corrected for the piping reduction. It basically nets less Cv than listed flow for equal pipe sizing. Also a good point about the ball and characterizing discs. The bypass port on a Belimo (B) port is rated at only 70% of the A to AB port. Just a little reminder.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •