Good point; For that reason maybe the " 3 " inch valve would be more suitable in this case. (to insure required flow to the chiller in bypass). I think I have all the infomation necessary to select the proper valve.
One thing that I am sure of is, that the selection has not been "botched"
"Orion242--It will only be oversized if you botch the selection....."
Thanks guys I have learned a lot
-
09-25-2008, 01:01 AM #15
Regular Guest
- Join Date
- Jun 2007
- Posts
- 134
I am in no way a valve expert, but have picked up a few things along the way. If the pipe is 4" and you do place a 3" or even 2 1/2" valve in line, I know the Cv must be corrected for the piping reduction. It basically nets less Cv than listed flow for equal pipe sizing. Also a good point about the ball and characterizing discs. The bypass port on a Belimo (B) port is rated at only 70% of the A to AB port. Just a little reminder.