Thread: NAE 5520
    San Jose, CA
    NAE 5520
    I have a NAE with multiple trunks. One trunks 23 TEC non programmable tsats(MS/TP) with an EOL that I mapped today. I created a fieldbus trunk. This worked fine.
    Trunk 2 is TEC stats as well. (VVT) I have not been able to get these mapped in.
    My question is what type of trunk do I create?
    1. fieldbus
    2.bacnet fieldbus
    It is 4.0
    Thanks!!
    By the way I have been starring at the directions all day and just looking for some help.
    you need to add a Field bus for bacnet.
    hi-lite the nae.
    select insert integration and select field bus.
    name is as field bus 2.
    you will need to select the hardware tab and change it to bus 2 to save it.
    Nov 2005
    Shreveport, Louisiana
    Which trunk is the LonWorks trunk?
    UA Local 141
    Nov 2005
    What type of tec's are on the other trunk?
    UA Local 141
    San Jose, CA
    Trunk 3 is the dedicated Lon trunk which has already been completed with the 2 Voyagers onsite.
    Here is a link to the VVT setup
    http://cgproducts.johnsoncontrols.co...c=1449&req=tec
    Check it out and let me know what you think!!
    This is the install document and point map.