Which heat is run during heatpump defrost ?
I've got the TH8320 honeywell tstat.
Which heat is run, aux or emergency when the heat pump (Amana ASZ140361) begins its defrost cycle ?
The tstat is setup as 3heat/2cool (though there isn't 2 cooling stages.)
Thx.
Adam
-
09-16-2008, 01:25 PM #2
Professional Member
- Join Date
- Apr 2005
- Location
- NE PA
- Posts
- 697
In nearly all systems, Aux heat and emergency heat are the same thing. In some bigger systems, the Aux heat may be staged, but again the same elements are used.
paul
-
09-16-2008, 03:31 PM #3
and.....
the defrost call comes from the control board, not the t-stat.
-
09-16-2008, 03:50 PM #4
Regular Guest
- Join Date
- Feb 2008
- Location
- Lucas, TX
- Posts
- 103
I see;
So it depends on how the installer hooked it up.
Thanks.
Adam
-
09-16-2008, 07:21 PM #5
Regular Guest
- Join Date
- Jul 2008
- Location
- Dutchess County, NY
- Posts
- 152
usually the aux heat comes on while the HP is in defrost. when there is a call for defrost the HP automatically locks itself out, at that point the HP will put out a W2 signal... enabling aux heat..
Last edited by Sonicview; 09-16-2008 at 07:40 PM. Reason: k
-
09-16-2008, 10:01 PM #6
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
-
09-16-2008, 10:24 PM #7
Regular Guest
- Join Date
- Jul 2008
- Location
- Dutchess County, NY
- Posts
- 152
ok... technically speaking..it doesnt really "lockout". Defrost mode is identical to cooling mode except that the outdoor fan motor stops and auxilary heat is turned on to continue heating the house.
Defrost is engaged by the defrost control board and utilizes a temp/timer control which includes a field adjustable time period between defrost cycles of 30 60 or 90 minutes...
So , airmechanical is correct...it does continue to run but, it is just not heating the house, it is defrosting...but essentially the HP is "locked-out" from providing heat,... so, it enables auxilary heat until it has completed it's defrost cycle.
-
09-16-2008, 11:00 PM #8
Since HPs and aux heat can be locked out.
You shouldn't use term locked out to describe HP defrost operation.
It will just confuse to many people.
-
09-17-2008, 06:18 AM #9
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
-
09-17-2008, 03:24 PM #10
Regular Guest
- Join Date
- Jul 2008
- Location
- Dutchess County, NY
- Posts
- 152
-
09-17-2008, 08:26 PM #11
Professional Member*
- Join Date
- Oct 2006
- Location
- The Beach
- Posts
- 459
Reversing Valve
Surely we all know what the reversing valve does during the defrost cycle.