Honeywell IAQ Dehumidify Question
I have read various posts of people with similar problems but I cannot get my IAQ to succsessfully use my A/C to dehumidify. I have ...
Furnace: Carrier 58PAV135-20 series 151 (single stage)
A/C: Carrier 38CKB060300 (single stage)
Humid: April Aire 600 [currently not connected in order to simplify setup pending resolution of dehumid problem]
First off, I have no experience wiring this level of complexity tstat, but with such a basic setup, I figured there would be little problem.
My IAQ is set to fan(auto) and system(auto) with dehumid set to 45%. The heat temp is set to 65 and cool to 77. The current indoor humidity has been between 60-70% all day and the A/C will kick in reducing the indoor temp to 3 degrees below the cool setpoint (as per setup function 0383 I assume) but will not continue cooling to reduce the humidity.
What strikes me as odd is that on the dehumid screen, the AUTO/OFF option is present ... even though setup function 0379 (dehumid control) is set to 1 (dehumid with AC). The Operating Manual (p18) specifically indicates that AUTO/OFF option is only present when using a whole house dehumid and is not present when dehumidifying with the AC.
For clarity, I have the AC wired to Com and Y only, not DHM.
Any and all help is greatly appreciated.
Todd
-
09-14-2008, 11:09 PM #2
diy not allowed here.......
-
09-14-2008, 11:22 PM #3
You need some modifications to your unit.
The IAQ will run your system to cool, but since you don't have a VS blower for it to slow down, it won't be able to actually dehimidify.
Any competent contractor, can easily make teh alterations for you.
-
09-14-2008, 11:23 PM #4
New Guest
- Join Date
- Sep 2008
- Posts
- 2
Allow me to clarify DIY-"appearing" thread:
I just bought this house about two months ago. The sellers provided proof of "maintenance check" of HVAC system as condition of sale. Now that the deal is done, I have noticed the peculiarity described. I have contacted the company that performed the maintenance check and they will come out to check my concerns ... for $75. Before I invest this money, I want to know if I have a legit concern or if a simple incorrect setting was originally missed.
-
09-16-2008, 08:37 AM #5
Professional Member
- Join Date
- Feb 2003
- Location
- garland, texas
- Posts
- 540
A maintaince check to the person selling the home my only mean change the filter, clean the condenser, blow out the drain, and verify there is some refrigerant in the system, I do not want to spend anymore money on this house I'm selling it. A maintaince check is usually interpreted by the home buyer to mean the a/c is correctly sized for the house, everything is running like a fine swiss watch and my utility bills will very low.
-
09-16-2008, 11:32 AM #6
Without getting into the detail of equipment, here are a couple suggestions. Over cooling 3^F is the t-stats simple way of dehumidifing. The basics of maxing the moisture removal of the a/c is slow the air flow over the cooling coil to all the coil to get cold enough. Coil temps of 45-50 remove more moisture. The limitations are coil freeze-up and sweating ducts. Typically, you need enough cooling load to remove 5-8 gals. of moisture per day to maintain <50%RH. A 3 ton a/c removes a gallon of moisture per hour. 5-8 hours of cooling is needed at a minimum to maintain <50%RH. Cooling to 78^F with a 3^F over-cool for dehumidification will not get you to <50%RH during wet cool weather.
Using a whole house dehumidifier like the Ultra-Aire will get you <50%RH during low/no cooling load conditions. These units are added to your a/c. The dehu with a well tuned a/c will provide any temp/%rh combination you want. Check my posts for more discussion. Regard TB
PS I use a system similar to yours and have posted data.Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
09-17-2008, 12:30 AM #7
Why do you have the IAQ on a very basic single stage non-variable speed furnace.
-
09-17-2008, 12:35 AM #8
Maybe he plans to get a VS furnace later.
And doesn't want to pay for a stat twice?
-
09-17-2008, 08:36 AM #9
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
-
09-17-2008, 09:23 AM #10
-
09-17-2008, 02:53 PM #11
Regular Guest
- Join Date
- Jul 2008
- Posts
- 550
What role does the TXV play in this? What about the TXV helps dehum?
-
09-17-2008, 04:30 PM #12
-
09-17-2008, 04:41 PM #13
Regular Guest
- Join Date
- Jul 2008
- Posts
- 550


Reply With Quote