    Tried the new Rheem out this morning

    well it was 40 degs here this am so I tried the new furnace. I was impressed that the temp of the air coming out of the register was as hot as it was. Everyone told me it would be much cooler than my old oil furnace. It seems hotter !

    I checked it with a digital thermometer in the reg and it was 130 degs . Now this was with the furnace in second stage because the t-stat said the room temp was 64 and I set it at 70.

    Seems to have performed great now lets see when it is below zero out

  2. #2
    Join Date
    Aug 2008
    Posts
    13
    Post Likes

    DELTA T

    THIS MEANS YOU HAVE A 66 DEGREE TEMP DIFFERENCE OR(DELTA T) IF YOU LOOK INSIDE YOUR FURNACE AT THE DATA PLATE IT WILL TELL YOU WHAT THE TEMP DIFFERENCE SHOULD BE, THAT WILL TELL YOU IF THE FURNACE IS OPERATING PROPERLY

  3. #3
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    2,931
    Post Likes
    Hotter is not better; the greater the temperature rise is, the less efficiently the heat exchanger can transfer heat from the combustion gasses to the indoor air. Life span can also be reduced.

    66F is probably on the high end of the specified range - check the dataplate.
    I've discovered a natural law - everything gets progressively worse. Things only break down and become depleted. Life isn't worth living and everything is going to hell.

    Death is the messiah. Everything else is irrelevant and arbitrary.

  4. #4
    Join Date
    Apr 2008
    Location
    Upstate New York
    Posts
    799
    Post Likes
    ok plate says hi fire 40-70f low fire 30-60 does this make sense ?? It was in the hi fire mode and the temp was taken at the register right above the furnace in the living area.

    Is this ok or do i need to call them back and have it adjusted ????

  5. #5
    Join Date
    Sep 2008
    Posts
    89
    Post Likes
    Quote Originally Posted by cvcman View Post
    ok plate says hi fire 40-70f low fire 30-60 does this make sense ?? It was in the hi fire mode and the temp was taken at the register right above the furnace in the living area.

    Is this ok or do i need to call them back and have it adjusted ????
    The 66 DEGREE Temp split is between 40-70, so your ok. Just means air flow is slightly low. Depending on the blower, you may be able to increase the speed, but you may get a noisy unit.

    Let it go awhile. Should be OK. If you have to call them out for another reason, you can mention that you read that the blower may be able to be speeded up in heating speed. (Maybe not)

  6. #6
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    5,256
    Post Likes
    hope the filter dont get dirty, also with a high temp rise it tends to dry out the house more

  7. #7
    Join Date
    Apr 2008
    Location
    Upstate New York
    Posts
    799
    Post Likes
    It has the thicker 4" filter in it. I had the register in the basement closed would it help to open that reg ??

    I wouldn't mind it drying the house out some as it tends to be kinda humid in the winter anyway not real bad though.

    Is there a way they can change that temp rise easy ?? I know the fan was running at hi speed because when it only needs to go up like one deg in temp the fan is slower.

    If left at this temp rise would it do harm or really cu my efficiency ?? If so shouldnt I call them ??

    If the fan is already in hi that probably cant be chgd then right ??

  8. #8
    Join Date
    Aug 2008
    Location
    Indianapolis
    Posts
    41
    Post Likes
    depends on the system. could be variable speed in which case cfm can be adjusted or you may have three or four speed taps. high speed is usually reserved for cooling

  9. #9
    Join Date
    Apr 2008
    Location
    Upstate New York
    Posts
    799
    Post Likes
    its a rheem RGRL I believe it is a 2 stage 2 speed blower ??? Where is twilli when I need him

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    70,021
    Post Likes
    Quote Originally Posted by catmanacman View Post
    hope the filter dont get dirty, also with a high temp rise it tends to dry out the house more
    Temp rise has no effect on the humidity.

    Same amount of moisture in the air(grains per pound of air), at 40° rise, as at 70° rise.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    70,021
    Post Likes
    Quote Originally Posted by beenthere View Post
    Temp rise has no effect on the humidity.

    Same amount of moisture in the air(grains per pound of air), at 40° rise, as at 70° rise.
    Open the basement return, it will help to lower temp rise, to a safer level.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Apr 2008
    Location
    Upstate New York
    Posts
    799
    Post Likes
    I know this is stupid but the return is the hot air run correct ?? There is no cold air run in the basement just a hot air ??

    There are lots of cold air returns up stairs though

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    70,021
    Post Likes
    Return is the air drawn into the furnace.
    In heat mode, its the cold air.

    I'd still open the supply in the basement. It will help lower the temp rise, by lowering your supply static.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?