Page 3 of 5 FirstFirst 12345 LastLast
Results 27 to 39 of 54
  1. #27
    Aug 2008
    Thanks beenthere. Is that something I can see on the air handler? Or can you tell me that?
  2. #28
    Aug 2008
    Indianapolis
    if the AH has dehum contacts it needs to be wired right. some power up for dehum some dont honeywell does not. tell him there is no shame in calling honeywell and goodman, its their equipment and they know it best
  3. #29
    Not always easy to see on the air handlers.
    Best to ask them, if they wired it up.
  4. #30
    Aug 2008
    Its the goodman AEPF303616 variable speed air handler. I kinda wish I could check it myself. I asked them if the thermostat was hooked up for dehum before they left the first time and they said Yeeeah lol
  5. #31
    I know where the terminals are. But not allowed to tell you.
    its that DIY rule.
  6. #32
    Aug 2008
    Ok I'm not sure if they set the CFM but on the interface module of the thermostat, nothing is hooked to the DHM 1 or 2. I take it that means its not hooked up correct?
  7. #33
    Nope. It can't control blower speed without them being wired in.
    When you talk to them.
    Explain everything you want it to do, to them.
    They may not understand what you want it to do. Since they never used this stat before.
  8. #34
    Rochester, MN
    Is this a A/C only system or heat pump? Single stage or two stage?
    If it's two stage, hope they wired up the 2nd stage up right.
  9. #35
    Quote Originally Posted by sakit2ya View Post
    It was both. They found a jumper that corrected the problem. It will now cycle on and off as it is supposed to.
    I've had 2 Goodman variable speed air handlers do what you describe. I ended up finding an undocumented factory installed jumper wire on the control board causing the problem. Maybe the 2 I found were not isolated cases...
  10. #36
    Aug 2008
    Its a single stage heat pump with VS air handler. They are coming out this morning to wire in the DHM contacts.
  11. #37
    Rochester, MN
    Its a single stage heat pump with VS air handler. .
    Do you have electric heat back up on it? Staged?
    Also, not sure where you out of, if you do have electric heat back up and in a cold climite, they hook up an outdoor sensor?
  12. #38
    Aug 2008
    Im in SE GA hot climate. They came by this morning and hooked up a wire to the DHM 1, but it still doesn't seem like the air handler is slowing down for lowering the humidity. He wasn't sure if he needed the jumper from R to the 1s he said. Does he?
  13. #39
    Rochester, MN
    Yes, the tech needs to add a jumper from one of the R's down to DHUM1, then DHUM2 to the air handler.
    So do you have back up heat?