Hey Gang,
Can somebody explain how compressor lockout and recovery work?
From what I understand:
Compressor lockout is the temperature dictated by the stat that basically forces a hybrid system to run backup heat.
Now .. backup heat ... I'm assuming this behaves differantly if you have electric strips vs. a gas furnace?
The reason I ask is this. I have read on this forum a number of times where folks say they have their electric strips come on during the recovery phase in their heating cycle. It appears, to me the layman, that the strips either come on in tandem to the heat pump or they are coming on solo. There is never a mention of the lockout temp on the stat.
So what happens with a hybrid Heat Pump / Propane system? My assumption was, recovery or not, if the temperature outside was above my lockout setting the heat pump would run as long as it needed to in order to catch up. The gas furnace would only fire if the temperature was under my lockout set point.
Am I right?
-
09-10-2008, 03:26 PM #2
Lockout can be interpreted in more than one way.
High temp lockout: if outdoor temperature exceeds a given setpoint, compressor will not run if heat pump system is in heat mode. This is to prevent excessive head pressure building up in the indoor coil, stressing the compressor and system.
Low temp lockout: if outdoor temperature goes below a given setpoint, compressor will not operate if heat pump system is in heat mode. This setpoint is about equivalent to the "balance point" of the house, where the house structure is losing heat to the outdoors at about the same rate the heat pump compressor, by itself can bring heat in. Below that point, running the compressor does not accomplish much, so it is locked out and the back-up heat source is the sole provider of heat."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
09-10-2008, 03:49 PM #3
Professional Member
- Join Date
- Dec 2007
- Location
- East central Indiana
- Posts
- 477
In the case of gas/heat pump combinations, a "fossil fuel" kit is normally used. This is done for at least 2 reasons I know of. 1. To prevent the heat pump and gas furnace from operating at the same time, in which case the furnace would be blowing hot air over the indoor coil (no big deal in the case of electric furnaces, because the "draw through" application is used). 2. To prevent the heat pump from operating below a certain temperature (it would be rather pointless to use the heat pump below a certain temperature, because without the gas furnace being able to run simultaneously, the heat pump simply wouldn't be able to keep up).
Now, if it's pretty cold outside, and if the heat pump still isn't on low temp lock out, the stat will sense when the heat pump is "falling behind", and will turn on the furnace (with the fossil fuel kit turning off the hp at that point).
I'm probably goofing up somewhere, but when I make my own fossil fuel kits out of relays and temperature switches, that's what I design them to do.
-
09-10-2008, 08:08 PM #4
Regular Guest
- Join Date
- Mar 2008
- Location
- Jackson, NJ
- Posts
- 176
-
09-10-2008, 09:37 PM #5
Professional Member
- Join Date
- Sep 2007
- Location
- KY
- Posts
- 79
-
09-11-2008, 06:18 AM #6
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
-
09-11-2008, 08:42 AM #7
Professional Member
- Join Date
- Dec 2007
- Location
- East central Indiana
- Posts
- 477
-
09-11-2008, 11:13 AM #8
Regular Guest
- Join Date
- Mar 2008
- Location
- Jackson, NJ
- Posts
- 176
-
09-11-2008, 11:33 AM #9
-
09-11-2008, 11:45 AM #10
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
-
09-11-2008, 02:08 PM #11
Regular Guest
- Join Date
- Jul 2008
- Location
- Dutchess County, NY
- Posts
- 152
Ok first off..what kind of thermostat do you have? you stated that there was no mention of a lockout set point on your stat... some stats have hidden programming built in and are accessed by holding several buttons down for several seconds... anyway, the stat should have been programmed by your installer which would have included a lockout point for your HP compressor or if you have a zoned system that uses a zone board the lockout point could be set there. either way you would need an outdoor air sensor for this feature, so you can trace the wire back to see where it is going. Your compressor is also locked out if you ever put your stat in emergency heat mode. The reason for a lockout is that you never want to have both primary and auxilliary heating running at the same time. But you want your efficient HP to work for as long as you can get it to run efficiently ...right around 30° is where I find it not to put out enough heat for it to run any longer so you turn it off or "lockout" the HP and go to auxilliary oil/propane/electric/ etc. but When the outdoor temperature is between the two temperatures, both the Compressor and Auxiliary Heat operate with some stat models.
You also asked about recovery time.. again what kind of thermostat are you using? Recovery is displayed when the heating or cooling system is activated before a set point For example: Set the Wake time to 6 am, and the temperature to 70°. The heat will come on before 6 am, so the temperature
is 70° by the time you wake at 6. The message “Recovery” is displayed when the system is activated before a scheduled time period.
-