Thread: Creating a Filter Drier Loop Question

  1. #1
    Join Date
    Aug 2008
    Posts
    79
    Post Likes

    Creating a Filter Drier Loop Question

    My R22 system is about 15 years old. It has no filter drier on the liquid line. Nor anywhere else on the system

    What I would like to do is just run the system R22 refrigerant through a drier that is looped onto my manifold gauge.

    Where should I put the drier? On the High side or Low side of the manifold gauge? I would think the Hi side because that is where the drier normally goes on the system. This is however a bit different since it will loop through the manifold so not sure where it will be best to locate it. I will have a fitting on the low side of the manifold that will change the liquid to vapor. I am sure you have seen them. Imperial sells one called Qwik Charge.

    I know there will be questions like "WHY NOT" just put one inline on the unit now. I don't want to open the system to put one on for one thing. And for those who are going to say "WHY DO YOU WANT TO DO THIS" please don't. If that is the only input you can deliver on this question please don't bother to reply to it.

    I appreciate your cooperation and thanks you.
    Quick reply to this message Reply  

  2. #2
    Join Date
    Aug 2008
    Posts
    42
    Post Likes
    Whats for dinner? MEATBALLS!
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    LOL...

    But why would you think doing this is a good idea.

    Your not going to clean anything out of your system by doing it.

    Filter driers don't clean or dry systems in just a few minutes, or hours.
    Quick reply to this message Reply  

  4. #4
    Join Date
    Feb 2006
    Location
    Tn.
    Posts
    1,346
    Post Likes
    Why do you want to do this?
    Quick reply to this message Reply  

  5. #5
    Join Date
    Dec 2007
    Location
    East central Indiana
    Posts
    477
    Post Likes
    Is this a heat pump? Reason I ask is that most straight AC units usually only have one access valve on the liquid and suction lines. So there wouldn't really be any way to "loop" the dryer, right? But if it were a heat pump, then you could loop a bi-flow drier between the two high side access valves...I think...

    Problem is, I guess only half of the refrigerant would go through the dryer on each pass (the other half would go through the regular piping). But, oddly enough, this does seem like a really good idea. That way, a tech could just go out and slap on a dryer for maybe a month or two, and then just take it off, without having to recover, braze, recharge, etc. Let me know how it works out.
    Quick reply to this message Reply  

  6. #6
    Join Date
    Jan 2002
    Location
    Ft.Worth,Tx
    Posts
    4,809
    Post Likes

    Thumbs down DIY Or Rookie tech.

    He can't even spell right look at his name.

    Havactech?


    Need to pump down system; cut liquid line and install L.L. Drier , purge with nitrogen while soldering then vacuum system , and recharge according to plate on unit.
    'Life begins with the journey each day'
    Quick reply to this message Reply  

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Think how many service calls you could get.
    When people cut the hoses with their weed wackers. LOL

    .
    Quick reply to this message Reply  

  8. #8
    Join Date
    Jun 2008
    Location
    NC
    Posts
    30
    Post Likes
    Are you HUFFING???? Why do you want to do this???
    Quick reply to this message Reply  

  9. #9
    Join Date
    Jun 2008
    Posts
    1
    Post Likes

    free entertainment

    i was having a crappy day until i read this post Thank you "beenthere" i blew milk out my nose over the weed-wacking comment LOL !!!
    Quick reply to this message Reply  

  10. #10
    Join Date
    Aug 2008
    Posts
    79
    Post Likes
    Thread Starter
    I purposely chose that name. I should have expected a reaction like this because that is how most people are stupid and uneducated!!

    For the one and only one person who properly replied thanks.

    This is not a heat pump. It is a residential R22 system with two access ports one on the suction side and one on the Hi side.


    Your saying that liquid from the hi side will not loop back into the vapor (suction side)? Because if it will then it should work correct?


    I would connect it to the Hi side of the manifold? I asked this same question to an Engineer at Appion and he said rather than connecting a direr filter inline to the recovery system just loop it with the manifold and leave the recovery equipment out of the equation.
    Quick reply to this message Reply  

  11. #11
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    LOL, I love my resi friends for stories like these.
    Quick reply to this message Reply  

  12. #12
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    the unit has ran 15 years with out one i would leave it as is . if you do as you propose you will dump liquid at high preasure into the suction line and very likely damage your compressor
    Quick reply to this message Reply  

  13. #13
    Join Date
    Aug 2008
    Posts
    79
    Post Likes
    Thread Starter
    Won't happen. I have an Imperial Qwik Charge adapter. I will have it on the manifold suction side. So the liquid will enter through the drier and then pass through to the suction side if this will work in theory or not?

    I plan on doing it over a course of a few weeks, a few hours at a time. I will not leave it connected that way untended.

    Either way I can't get a definitive answer to this thread, so I will have to just try it!!
    Quick reply to this message Reply  

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    That quick charger, isn't designed to have 200 plus PSIG liquid feeding into it.

    It will over feed.

    Cut the system open, and install a LLFD the proper way.
    Quick reply to this message Reply  

  15. #15
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    917
    Post Likes
    I'm really curious as to what you are trying to do.

    Is there some contaminant that you are trying to filter out of the system or is it just to ensure that there is no moisture?
    Quick reply to this message Reply  

  16. #16
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    917
    Post Likes
    I'm really curious as to what you are trying to do.

    Is there some contaminant that you are trying to filter out of the system or is it just to ensure that there is no moisture?
    Quick reply to this message Reply  

  17. #17
    Join Date
    Sep 2008
    Location
    Central Virginia
    Posts
    17
    Post Likes
    I know that you said not to ask "why," but I can't help myself.

    In all honesty, why do you want to do this? You didn't say anything about the unit having problems or not operating properly.

    The unit has been running for 15 years without a drier, why does it need one now?

    For what it is worth, if it needs a drier, pump it down and install one. If it aint broke, don't fix it.
    Quick reply to this message Reply  

  18. #18
    Join Date
    Dec 2007
    Location
    East central Indiana
    Posts
    477
    Post Likes
    As long as you're not dumping liquid into the compressor, and as long as your pressures aren't way out of wack, I really can't see any reason why this wouldn't work. Even though you have a "vaporizer", I'd still be inclined to heed beenthere's advice. His responses are brutally concise, but always seem to hit the nail right on the head.

    But if you really do want to experiment (and what's the worst that can happen, you'll need to replace your unit. Hell with it, it's old anyway, and if it works, think of what you stand to gain) the way I'd do it would be like this: Right off the hi side port, put your drier. Then the vaporizer. Then into the suction line. (I tend to believe that driers can catch stuff better when the refer is in liquid form, but I could be wrong. Boss swears by suction driers and says liquid driers make as much sense as "putting air filters over the supply registers").

    Godspeed amigo
    Quick reply to this message Reply  

  19. #19
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes

    Hmm

    Quote Originally Posted by havactech View Post
    Won't happen. I have an Imperial Qwik Charge adapter. I will have it on the manifold suction side. So the liquid will enter through the drier and then pass through to the suction side if this will work in theory or not?

    I plan on doing it over a course of a few weeks, a few hours at a time. I will not leave it connected that way untended.

    Either way I can't get a definitive answer to this thread, so I will have to just try it!!
    let us know the results
    Quick reply to this message Reply  

  20. #20
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    What brand of unit, lots of manufacturers install a filter drier inside the unit, and it often doesn't look like the typical LL filter drier...
    Quick reply to this message Reply  

Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •