    Dehumidification Controls

    I normally do Dehumidification during Vent and Cooling Mode, so I stage on compressors and Hot Gas Reheat to maintain cooling setpoints. A customer request unit that can do dehumidication during heating mode as well. So should I stage on compressors and reheat to maintain heating setpoint?
    Another questions that I have is, why some control engineers bring on cooling to maintain Humidity level in the space but some bring on cooling to maintain a low suction pressure during dehumidification?
    Please help
    Thanks
    Natalie

  2. #2
    Join Date
    Mar 2003
    Posts
    7,249
    You must understand that simply raising the discharge air temp artificially "shows" dehumidiifcation simply by changing the psychometric conditions of the airstream. Actual dehumidification is accomplished with mechanical cooling or chilled water cooling. The reheat is to give you a false load so that you do not overcool the space while trying to lower humidity levels. As far as providing dehumidification while heating, you actually already are, but possibly not enough. As in the previous case, by heating the airstream, you change the psychometrics and lower humidity levels. If you nee further dehudimidifcation you could use mechanical but there are other ways to do it such as a wheel. I guess the real answer to your question is that every situation is different, equipment is different, and you need to plot your conditions on a psyche chart to see where you need to head to get to the desired conditions.

  3. #3
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    7,451
    What exactly is your application?
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  4. #4
    Join Date
    Oct 2007
    Location
    Houston Taxes
    Posts
    28
    Quote Originally Posted by DeltaT View Post
    What exactly is your application?
    It is a Constant Air Volume unit for a Grocery Store.
    Thanks

  5. #5
    Join Date
    Mar 2005
    Posts
    639
    sounds like you are using discharge gas from med temp rack as reheat , so in turn i would say you would tap off common liquid line med temp , for this dehumidification ,which all sizing would have to be calculated for rh load regards stan
    Keep it simple to keep it cool!