    No heat - AC works? Goodman furnace

    Hello all! I'm new here and would love some help.

    I have a 2 year old Goodman Furnace - it's a 95% efficent model that has the variable speed fan and 2 stage burner. (not sure the model # offhand)

    It's been a decent furnace, however last heating season I had issues with it heating - the igniter would not fire, so I hooked up a multimeter and found the igniter to be OK, but the main circuit board was bad from what I can tell. The place I bought the furnace from replaced the board at my cost.

    The A/C has been working fine all summer, and tonight being cool we went to kick on the heat only to have it not work.

    What will happen is when the call for heat comes in, the exhaust blower fan starts up for about 1 second then it shuts off and nothing else happens.

    The red LED just blinks continously. There is a greed LED on the circuit board that blinks very faintly, and that's it.

    I read on the schematic that if the LED is blinking cont. that means the 115V is reversed, so I hooked up the AC power leads the opposite way and tried it again, and what will happen is the exhaust blower kicks on for about 15-20 seconds (enough to get to full speed) and then it shuts down with no trys at a restart - only a cont. blinking red LED. the green one is blinking very faintly.

    with the 115V AC hooked up backwards - that's when i get the longer run time on the exhaust blower, but I tested and I'm feeding the 115V to the neutral leg on the circuit board. With it wired properly (it did work last season, but it doesn't now) it will only run that exhaust blower for a very short time and nothing else happens - no igniter, fuel or main blower action...

    Help? is my main circuit board fried again?

    One other thing I noticed is there is a slight high pitched buzz/hum coming from the circuit board when the fan was being energized, even with the fan unplugged.

    thanks for your help!

  2. #2
    Join Date
    May 2002
    Location
    MEDIA PA
    Posts
    1,390

    ?

    R you sure the board is wire correctly , It seems U are over your head and need a service tech to look things over

  3. #3
    Join Date
    Sep 2008
    Location
    MN
    Posts
    2
    I am very adept at working on wiring. The only reason I changed the 115V AC wiring was the red LED was blinking and saying it was reversed.

    I have a VOM and know how to use it. The board is wired right to the best of my knowledge and the heat did work before the cooling season... nothing changed other than the passage of time and setting the thermostats from heat to cool.

    (It is a 2-zone system and that part works fine - as the AC zoning worked great and in the heat mode the zone dampers are responding correctly.)

  4. #4
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,959
    This is not a diy site

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event