    Desuperheater - Air to Air

    Has anyone ever installed a desuperheater on an air-to-air heatpump system?

    Any thoughts/ recommendations/ feedback?

    These are obviously prevalent on geothermal but I can't seem to find a lot on air systems.

    Thanks

  2. #2
    Join Date
    Jun 2001
    Location
    DFW
    Posts
    683
    They used to be more common.

    Modern heat pumps run at a lower temperature that allows preheating of water, but will require supplemental heat.

    In an air-to-air system, you also run into issues with freeze protection that are not a problem with geothermal.

  3. #3
    Join Date
    Feb 2007
    Location
    out in the country
    Posts
    633
    I saw a desuperheater on an air to air HP once. The desuprheater was mounted next to the outdoor unit, it was well below freezing that day, the desuperheater made a very big ice cube because it had froze and busted due to the outdoor temp.

    Thats where the problem is, the design of a desuperheater requires being connected to the discharge pipe coming off of the compressor , thru the desuperheater, out of the desuperheater and into the reversing valve. Unless you have a geo or a triple split unit these connections will be outside. Most areas its not a good idea to have water lines outside and exposed.