    Turn the filter pd measuring back on. Record new and repeated fault codes.
    Call Carrier.
    Buy your contractor a copy of Manuals D and J.

    What was their explanation for the faults you recorded?

  2. #41
    Join Date
    Aug 2008
    Location
    Ridgecrest, CA
    Posts
    37
    Quote Originally Posted by beenthere View Post
    On both units.
    Set the temp down 5 or 6°, so all zones are calling. Then see what your static is with all zones open.

    Your statics you posted are still too high.

    post what they are with all zones open.
    Unit one with 3 zones all open the unit says the zones are at 15 or open

    SP is 1.14 High Stage


    Second unit with all four zones open

    Sp is 1.01 High Stage

  3. #42
    Join Date
    Aug 2008
    Location
    Ridgecrest, CA
    Posts
    37
    Quote Originally Posted by adrianf View Post
    Turn the filter pd measuring back on. Record new and repeated fault codes.
    Call Carrier.
    Buy your contractor a copy of Manuals D and J.

    What was their explanation for the faults you recorded?

    What is filter measuring PD?

    He said code 161 was from high SP which it clearly states....

    codes 31, and 32 high and low pressure switch open he never really explained....
    Zone2 sirflow limited shutdown occured this was in the living room where the vents were closed


    I did ask how they size the ducts if they used formulas etc... and he said he wasnt the one who did it but the figure it out using the voulme of the house...sq footage and ceiling heights etc....
    Last edited by MPNX2; 08-29-2008 at 06:03 PM. Reason: Added Content

  4. #43
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Quote Originally Posted by MPNX2 View Post
    Unit one with 3 zones all open the unit says the zones are at 15 or open

    SP is 1.14 High Stage


    Second unit with all four zones open

    Sp is 1.01 High Stage
    Way too high. The HVAC contractor didn't fix anything. And is probably hoping you let it drop.

    I hope he didn't mean that the duct work for both units combined is sized for 2300 CFM.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #44
    Join Date
    Aug 2008
    Location
    Ridgecrest, CA
    Posts
    37
    Quote Originally Posted by beenthere View Post
    Way too high. The HVAC contractor didn't fix anything. And is probably hoping you let it drop.

    I hope he didn't mean that the duct work for both units combined is sized for 2300 CFM.
    I ask him and he said no for both....

    These units are capable of 1750 each correct?

    I am not going to let it drop if he thinks so he is mistaken..neither will my GC. I do know the ducting is HUGE in the attic...

    What is a good SP? It records high anything over I believe...so what is acceptable and is this published anywhere?

  6. #45
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    What you call hugh, and what is undersized, may be the same thing.

    I don't remember if you said if you have duct board, flex duct, or sheet metal.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #46
    Join Date
    Aug 2008
    Location
    Ridgecrest, CA
    Posts
    37
    Some is flex the other is covered with insulation and its stiff so I assume its sheet metal...some pictures











    In the last picture where the 2 PVC pipes enter the unit there is cool air leaking should this be sealed?

  8. #47
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    The filter SP notice will demostrate something is a rye by constantly telling you to replace the filter even though you just did.

  9. #48
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    If thats an N coil, I don't think your suppose to have the right side(top in this case) over hang the furnace.

    Bet you have a high PD with that coil set up. Weather or not it an N coil, thats a bad mount.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #49
    Join Date
    Aug 2008
    Location
    Ridgecrest, CA
    Posts
    37
    Quote Originally Posted by adrianf View Post
    The filter SP notice will demostrate something is a rye by constantly telling you to replace the filter even though you just did.
    He said he had it setup for EAC on a timed basis...

  11. #50
    Join Date
    Aug 2008
    Location
    Ridgecrest, CA
    Posts
    37
    Quote Originally Posted by beenthere View Post
    If thats an N coil, I don't think your suppose to have the right side(top in this case) over hang the furnace.

    Bet you have a high PD with that coil set up. Weather or not it an N coil, thats a bad mount.
    I dont know what the coil is in that pictures....great this keeps getting worse..

    What is PD pressure Drop

  12. #51
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Quote Originally Posted by dash View Post
    They must hve set it up for a time based notice,the tru sensing dirty filter alert,would being going off daily,with your static .
    This quote is from the Carrier Infinty Maven.

    They are masking the problem this way, sorry.

  13. #52
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Quote Originally Posted by MPNX2 View Post
    I dont know what the coil is in that pictures....great this keeps getting worse..

    What is PD pressure Drop
    Yes.
    PD pressure drop.

    You need to think about requesting a Carrier rep come out with the contractor also.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 4 of 7 FirstFirst 1234567 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event