Parallel System
Hey Guys
Working on a 140 Horsepower Hussman Rack R-22 rack system. If the system is running 100% all 5 evaps and all condenser fans all compressors what should the receiver level be running at?
Thanks Tim
-
08-20-2008, 07:57 PM #2
-
08-20-2008, 08:53 PM #3
Professional Member
- Join Date
- Mar 2003
- Location
- Cochrane, AB
- Posts
- 504
Please give my the linear footage and diameter of all liquid and suction lines connected to the rack (rounded to the nearest foot) as well as all m/n #s of every evaporator and condensor. I also need a count of every pipe fitting used and the exact ambient temperature and size of the receiver, then I'll guess.
I hope you get my point, there is no answer other than 'not empty'
-
08-20-2008, 09:34 PM #4
Professional Member
- Join Date
- Feb 2003
- Posts
- 1,165
As mentioned there is no exact %, the level will vary depending on ambient temps. and load demand. Typically the receiver level might range from 20 to 50% depending on the extremes of your climate. Most receiver level alarms will trip at below 10% after timeout and stop timing out at approx. 15%.
If the systems are all stat/solenoid controlled as it sounds like then the level would vary more than an EPR controlled system, proper receiver and condenser sizing would also play a role in the final equation, depending on all the variables (somewhere between 15% and 80%)
Watts New, Ohm My, I been Electrically Commutated. Are U2.
-
08-21-2008, 10:08 AM #5
Professional Member
- Join Date
- May 2008
- Location
- Jacksonville
- Posts
- 61
Thanks for the replies guys I will get the info as sson as possible as i am in jacksonville and we are getting soaked with this tropical storm at the present.
Thanks Tim