    bad txv or bad suction valve

    How can you determine which it is?

    Scrolls don't normally pump down.

    I seem to remember, a bad suction valve will have low SH.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Scrolls can pump down and don't have valves.
    Look up the performance curve for the vompressor

  3. #3
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    usually they bail at 30 or 40 psi

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by timjimbob View Post
    usually they bail at 30 or 40 psi
    No usually they pump down unless it has a LPS which you can jump out. Scrolls don't have valves.

    Generally txvs fail in the closed position with low suction pressure and high superheat. I have seen them fail open though. What's your subcooling?

    Low superheat is usually due to low airflow or overcharge.

  5. #5
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    SH 40 SC9

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by timjimbob View Post
    SH 40 SC9
    More than likely bad txv
    Heating/Cooling Services Inc.
    www.heatingandcoolingservicesinc.com

  7. #7
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,907
    Post Likes
    Quote Originally Posted by jtrammel View Post
    No usually they pump down unless it has a LPS which you can jump out. Scrolls don't have valves.
    I've had many which opened the IPR when suction pressure was still over 100 PSI. That stinks because I have to recover the refrigerant for a repair on the indoor coil.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  8. #8
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    What is the evap SH? The SH should be the same, KindaSorta, a 10* SH should still be 10* w / leaking suction reeds or even a leaking scroll. Little leakers,

  9. #9
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    Quote Originally Posted by kdean1 View Post
    I've had many which opened the IPR when suction pressure was still over 100 PSI. That stinks because I have to recover the refrigerant for a repair on the indoor coil.
    Air conditioner or heat pump?

    Most air conditioners don't have enough volume in the condenser coil to pump down and hold the factory charge. IPR will generally open in this case. York started putting labels on their ODUs warning technicians not to attempt a pump down.

  10. #10
    Join Date
    Dec 2006
    Location
    phoenix
    Posts
    303
    Post Likes
    SSH way too high and SC may be normal which means TXV or drier or restriction. Some OEMs want 10-20 SC depending upon unit. Bad suction valves will have roughly normal but never low SSH. To me the scroll vs a recip does not apply hear.

  11. #11
    Join Date
    Jul 2015
    Posts
    37
    Post Likes
    I've pumed down all scrolls... that hold. Internal check valve.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •