Older Carrier Flowtronic
Carrier Chiller M/N-30GB125-650 is displaying code/fault 61 which is a water low flow fault. I replaced the flow switch and it still had the fault. I jumped across terminals 13 and 14 on the microprocessor board and it still cut out on 61. Is it more likely to be the processor or actual flow?
If I tell you how long I have been in this business, would it really matter?
-
08-18-2008, 07:06 PM #2
Regular Guest
- Join Date
- Jul 2008
- Location
- ATL
- Posts
- 56
Did you check presure drop across the barrel with the same gauge and check it the design drop which should be written on inside of the controll panel .To veritfy you have enough fulid across the barrel.
-
08-18-2008, 07:52 PM #3
Professional Member
- Join Date
- Sep 2003
- Posts
- 154
-
08-18-2008, 08:39 PM #4
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,510
An open flow switch will give you a code 26
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-18-2008, 08:48 PM #5
Professional Member
- Join Date
- Mar 2008
- Location
- NC
- Posts
- 1,333
-
08-18-2008, 09:16 PM #6
the entering sensor is at the bottom of the barrell, the leaving is in the leaving side pipe. if the entering reads lower than leaving you will get a low or reverse flow. the sensor ought to be matching or close to it. on low flow the sensor at the bottom of the barrell will get colder due to location than the leaving water sensor. you can leave the chiller off for a little while and check the voltage drop on each sensor and compare it with the chart and see what it is reading.
-
08-18-2008, 09:34 PM #7
Regular Guest
- Join Date
- Sep 2005
- Location
- Boston
- Posts
- 66
The old code 61 could be faulty barrel thermister and or the compressor thermister, crossed thermister sensor connections at the board, a bad microproccessor board "not likely", a chilled water valve closed, or someting simple like a coupling on the chilled water pump has failed.
Carrier wisely advises against jumpering anything; however, we all know it is neccessary from time to time.
-
08-18-2008, 09:46 PM #8
From page 32 of the Carrier Flotronic Reciprocating Liquid Chillers manual dated 8-89. In part:
CODE 61, NO COOLER FLOW -----blaa, bla, bla then half way down it says "When there is no cooler water flow and the compressors are operating, the leaving water temperatue themistor will indicate no temperatue change. But the temperature of the entering water will drop rapidly and the entering water thermistor will detect this. When the entering water temperature drops to 5 F below the leaving water temperature, all the compressors will stop and code no. 61 will be displayed. bla..bla
Then: the error will be caused either by no cooler flow or if the wate is flowing in the wrong dirction through the cooler or if the thermistors are insstalled backwards."
I sure hope you have taken over one of my accounts that I have kept going now for close to 10 years on one of these system!
This customer had the same problem. After chasing down every friggin wire through every friggin panel, checking this and that he remembered that he had changed the supply pump...and he put it in backwards!
The Carrier Catalog number for this manual is 533-044."The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
- Alexis de Toqueville, 1835
-
08-18-2008, 11:24 PM #9
Short on BTU's?
If you have the flow, then it's probably low load.
As I recall, the water side sensors rarely were a problem.
I remember one that would do it on low load even with a decoupled primary.God Bless the USA
-
08-18-2008, 11:41 PM #10
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,510
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-19-2008, 05:01 PM #11
Professional Member
- Join Date
- Jan 2007
- Location
- Greensboro, NC
- Posts
- 128
Flow Issue?
If your thermistors checkout O.K. then you may have a flow issue. If you have an "open loop" system where sediment and trash can enter the barrel you may have enough build-up in the bottom of the barrel to restrict the waterflow in the area of the thermistor.
I have seen this probem several times, but only on open loop process systems.
Most of the time the thermistors just drift out of control range and need to be replaced. The early model 30GB had the thermistors inserted directly into the water or refrigerant circuit!
The newer models used a well to insert the sensors into.
Voltage test is OK.... inserting the thermistor into a cup of water with a thermometer and using an Ohm meter with the resistance scale has always proved to be extremely accurate.
-
08-19-2008, 08:29 PM #12
Professional Member
- Join Date
- Sep 2003
- Posts
- 154
The entering water t-2 was 10 degrees off according to the voltage chart. Replaced it late this afternoon and did not display 61 anymore but I'm still concerned because according to the voltage readings I have now the entering is still 5 degrees low and leaving is 5 high. What is the tolerance on these thermistors?
If I tell you how long I have been in this business, would it really matter?
-
08-20-2008, 08:58 AM #13
Professional Member
- Join Date
- Jan 2007
- Location
- Greensboro, NC
- Posts
- 128
Carrier Thermistor Checkout Voltage vs. Temperature
I know it is more trouble to check the thermistors with the temperature/resistance method... but I have always gotten poor results using the voltage method even with a Fluke meter.
Keep in mind, using either method, the type of connection used for terminating the wire on the circuit board. Invest in the proper tool for inserting the wire into the "connector". I think the board connectors were designed by either Hoover or Eureka.
The early Carrier books said the thermistors checked good or bad....nothing in-between. Most will go out a few degrees causing trips on flow, or oil foaming due to low superheat. A quick test before a lead compressor is replaced due to low oil pressure is to "temporarily" relocate the thermistor over the oil pump to the "plug" side of the suction service valve. This will add superheat to circuit due to the thermistor not seeing the heat from the motor barrel.
Again, be cautious of the unit not having wells for the sensor. They can be purchased from your Carrier dealer and you will make life easier for yourself and others by installing the wells to house the sensors. Later models of the 30GB already have them.