Results 1 to 6 of 6
08-16-2008, 03:30 PM #1
Professional Member*
- Nov 2001
- east kansas
- 7,969
120 vac fire damper, spring return/shut
Should 120 vac fire damper acuators have disconnects so a guy can service them?
Beware of advice given by some guy on the Internet.
08-16-2008, 03:55 PM #2
no .......what if you check a floor and forget to repower it .just disconnet the power wire at the 1900 box or within the damper actuator.
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
08-16-2008, 10:38 PM #3
No. The most you can hope for is a rib relay, a manual reset high limit, and an on/off switch.
There's not really much to do to those things. If you have 120v present at the motor, and it's not opening, get a new actuator.
08-17-2008, 12:07 AM #4
- Nov 2001
- east kansas
- 7,969
Got that. Except for the on/off switch.
Every once in a while after a power outage a couple of dampers wont open. I was calling the on/off switch a disconnect. None of them have it. I was thinking about installing an on/off switch when I exercise the actuator. Usually just pulling the hot works.Beware of advice given by some guy on the Internet.
08-17-2008, 08:22 AM #5
- Feb 2004
- SW Florida
- 1,243
That type of damper is called a combination fire/smoke damper (fsd) as opposed to a curtain-type fire damper (fd). They "fail" to the default position of closed when not energized. If there is not a dedicated fire control panel, they should be wired directly into the air-handler fan circuit,controlled with a firestat or a duct smoke detector. You then kill the FSD power by disconnecting the AHU circuit for servicing.
08-18-2008, 01:15 PM #6
- Dec 2005
- 107
Various control panels and test switches are available as options on the dampers. They should be specified more but rarely are.