Results 1 to 9 of 9
Thread: Twinned Carrier Issue
08-15-2008, 08:43 PM #1
Ive got two Carrier Furnaces Model 58tx155---11120 twinned together and having an issue with the blower relay on the primary unit chattering. The only thing that gets it to stop is pulling the wire that connects the two units. Both work perfectly fine individually but when connected together I have the afore mentioned issue . Figuring it was the primary units control board I replaced it but the problem is still there.Spent most of the day today getting beat up by this problem today an help would be appreciated. Thanks
08-15-2008, 09:54 PM #2
- Nov 2002
- amherstburg ontario
- 135
Are they twinned using a factory kit or are they twinned using field installed isolation relays?
08-16-2008, 07:00 AM #3
- May 2005
- smyrna ,georgia
- 34
i had the same problem,,you have to make sure the 115 volt line feeding
the furnace is pulled off the same leg or side of the power panel to the house or space,,( that means two seperate feeds off the same bus of the panel) you cannot have one 115 volt line coming in and split it for both furnaces,,it wont work.also make sure equipment grounds are installed.
later jaybetter to be thought a fool than to open ones mouth and confirm it
08-16-2008, 11:41 AM #4
Was thinking along those lines but wasn't sure if it made a difference. The school recently had a major electrical upgrade all new main switch gear and panel, ect. Originally was single phase but now its 3 phase. The units are twinned using isolation relays.
08-16-2008, 11:47 AM #5
- May 2005
- smyrna ,georgia
- 34
pull the cover off the panel and make sure your coming off the same buss or leg
that will remedy the problem
08-16-2008, 01:03 PM #6
http://www.johnsoncontrols.com/publi..._controls.html
I have used these twinning kits and never had any trouble"Paddle faster, I hear banjo music"
08-18-2008, 01:22 PM #7