Thread: To FLUX or not to FLUX

  1. #1
    Join Date
    Oct 2002
    Posts
    9
    Post Likes

    To FLUX or not to FLUX

    I use only silv 45 on copper to steel joints, been talking to another tech who uses 45 and white flux. I don't like the idea of any thing getting inside of the refer system which I'm sure some of the flux does.
    Are there any standards on this practice, or is up to the individual.

  2. #2
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    FLUX IT...your hitting the pipe with a 1500F flame clean and quik next joint
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Oct 2002
    Posts
    9
    Post Likes
    Thread Starter
    No worry about the flux contaminateing the system? . Ya thats the reason he says he uses it for the quicker process.

  4. #4
    Join Date
    Apr 2008
    Location
    Mesquite(Dallas), TX
    Posts
    50
    Post Likes
    Always use flux - makes for a quicker-cleaner and solid joint. I've done it this way for years and never had a problem.

  5. #5
    Join Date
    Jun 2001
    Location
    Greeneville, Tennessee
    Posts
    354
    Post Likes

    Flux

    I have used flux for this type brazing, as you mention, for over 25 years.

    No need to worry, except, clean the outside of the brazed connection as best as possible once completed.

    I usually clean with water then sand off or file off any excess flux. Otherwise, you will have corrosion set in over time. Plus a good visual to make sure you have capped the brazed joint solid! Telescopic mirror a must.

    Make sure you leak test!! After the repair you should evacuate, so make sure you are leak free or otherwise you will introduce moisture into the system!

    Depending on how you can isolate the system, you could always run nitrogen through the system while you braze which will prevent oxidation inside the piping. This is always a good practice, but rarely performed including myself! Evacuate the isolated portion of the system after nitrogen has been introduced into the system, to make sure all non condensible's are removed.
    Last edited by dgruber; 08-16-2008 at 08:44 PM. Reason: Added info
    Dealing with Global Warming

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •