chaterring LLS on WIF
I ran across a small WIF that was only able to get to 20F. Tstat was calling so LLS was open and unit running. Once I got back to the roof the liquid line was making all this chatter. I ran back downstairs. to discover the noise coming from the LLS valve. While energized the coil chattered like heck, stop for a while, then chatter a lil more then stop, etc . Customer said the chattering noise has been happening for sometime off and on.
Can those plungers get 'stuck' inside the valve? (This unit has had multiple surgeries) OR...Is there such a thing as a weak coil? Yes proper voltage was delivered to coil.
-
10-12-2008, 09:36 PM #2
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473
I carry a permanent magnet made for forcing open a sporlan LLSV. Its a good way to test if the problem is the valve or the coil. Is the coil a 24v one? If so the transformer may be overloaded at times causing the chatter. If its line voltage and as you say you are reading good power w the coil energized I would buy a new LLSV and coil w the understanding from my supplier that I will return one or the other. Then replace the coil first if that does it great. Else pump it down and change the valve.
-
11-27-2008, 11:36 AM #3
Professional Member*
- Join Date
- Nov 2000
- Location
- Memphis TN USA
- Posts
- 6,945
Where did you get that magnet? I have seen them before. I want to put it on my christmas list. Boss gives us $250 for christmas. I buy 1 bottle of Wellers and spend the rest on tools.
If the superheat ain't right it ain't charged right.
-
12-01-2008, 06:13 PM #4
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473
-
12-03-2008, 03:56 PM #5I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
12-03-2008, 04:36 PM #6
Professional Member
- Join Date
- May 2008
- Location
- S.E.Virginia
- Posts
- 87
CPS makes one. I have used it on Sporlan and Danfoss LLS .....works great Cost about $35.00.