Thread: Can I have 2 thermostats connected to my system?

  1. #1
    Join Date
    Sep 2006
    Posts
    136
    Post Likes

    Can I have 2 thermostats connected to my system?

    I have an dual fuel system (American Standard Heritage 16 HP, Freedom 80 furnace) and an Honeywell IAQ thermostat.

    What I would like to do is have a thermostat or sensor on the 2nd floor so that I can heat or cool the bedroom area to specific temperature at night.

    I have looked at having a Honeywell sensor added to the 2nd floor. That seems like the easiest solution. However, the tstat allows either the tstat, the sensor or an average to dictate the temp. But that is part of the setup and not the program, so I would manually have to change the setup each night and I ain't doing that!

    So I was wondering if a 2nd IAQ could be added and if either called for heat or cool, the system would respond. Is that possible? And would I have the 2 tstats wired to to 1 EIM or would I need to have 2 IAQ's and 2 EIM's and have both EIM's wired to the furnace?

    Or could I have a zone controller installed, but with nothing connected other than the tstats?

    Or is there some sort of timed switch I could have installed to switch between the 2 tstats?

    Of course this type of set-up would cause cooling in unoccupied areas and is certainly not efficient and a zone system would be the perfect solution. However, comparing the cost of a zone system to this option, the break even is a long, long time!
    Thanks,

    Mark

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Not worth the headache.

    Have you tried using the fan circ feature to even out the room temps.

    You could have the sensors added, to use averaging.

  3. #3
    Join Date
    Sep 2006
    Posts
    136
    Post Likes
    Thread Starter
    beenthere:

    I actually leave the fan on all the time and it does a decent job of averaging out the room temps. It does much better at night than during the daytime. And doing what you suggest is most likely the best easy solution.

    BTW, what would the headaches be in having 2 tstats? Curious minds and all that stuff!
    Thanks,

    Mark

  4. #4
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by markf57 View Post
    beenthere:

    I actually leave the fan on all the time and it does a decent job of averaging out the room temps. It does much better at night than during the daytime. And doing what you suggest is most likely the best easy solution.

    BTW, what would the headaches be in having 2 tstats? Curious minds and all that stuff!
    Be like having two brains in different locations telling you how to act. It didn't work for Steve Martin and it won't work for you.
    Training is important!
    Practical Training is a must!

  5. #5
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    To make this work you would need to install zoneing dampers and tie them into the second thermostat.

  6. #6
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by Tiger93rsl View Post
    To make this work you would need to install zoneing dampers and tie them into the second thermostat.
    this is the most correct answer to his problem!



    .

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by markf57 View Post
    beenthere:



    BTW, what would the headaches be in having 2 tstats? Curious minds and all that stuff!
    Isolation and lock out relays, so both stats can't call at the same time for different modes. Or back feed each other

    Short cycling because one stat restarts the system 10 minutes later.

    Temp over and under shooting temps because the stats can't calculate an accurate run time because the other stat keeps the HVAC running when it thinks its off.

    Finding a tech that doesn't pull his hair out when you have a sevrice problem with it.

  8. #8
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    A while back I was involved with a job like this. Boss installed a huge toggle switch the HO threw to select which stat (up or down) to control the system.

    Goodman has an aftermarket zone system that looks easy to cut in. I don't remember the brand.

    I thought Carrier had a programmable zoning kit. It's been a long time since I've looked at one. I would think a guy could install the controllers without the dampers
    Beware of advice given by some guy on the Internet.

  9. #9
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    In fact April air makes a zone kit that uses regular stats. Just install the panel without the dampers if you want to cut the costs.

    You would have to overcome the dual fuel challenges. Maybe Goodman's dual fuel kit might work.
    Beware of advice given by some guy on the Internet.

  10. #10
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    Lennox had a zone kit that uses regular stats also. I've never set one up. But I think it's my turn next.
    Beware of advice given by some guy on the Internet.

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Most zoning companies have panels that could be used with out the dampers.

    The zone panel would act as the isolation lock out relay.

    Very expensive solution to over cool or heat one area to make teh other comfortable.

    Cheaper to just set the stat higher or lower to make the other area of the house the temp you want.

  12. #12
    Join Date
    Apr 2007
    Location
    Tucson AZ
    Posts
    86
    Post Likes

    Huge toggle switch

    I've actually looked for such a switch, without sucess.

    Any idea where I might find one?

    I used to have some pretty weird stuff I'd concocted in homes I owned.

    Since I always had to de-weirdify them when I sold, I strongly resist
    the tempation.

    And I've thought of home building a thermostat switchover device with
    a bunch of relays or even a solid state version with analog switches.
    But just a big honking toggle switch would be a cleaner solution.

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Averaging sensors.
    You wouldn't have to remove them when you sell.

  14. #14
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    Post Likes
    Quote Originally Posted by beenthere View Post
    Averaging sensors.
    You wouldn't have to remove them when you sell.
    BT can these sensors be used in conjunction with a Infinity controller and Infinity furnace ? I have my kitchen that is always alittle colder than the rest of the house on the coldest days in the winter and would like to know how this would work if it is possible to have installed with one sensors in my kitchen and one in the main part of the home with 1 up stairs. Could you explain how these work ?

  15. #15
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    4,744
    Post Likes
    I've done this before twice. Each of them differently. One time was on a 4 zone Honeywell zone board with 8 thermostats hooked up to it. I simply used a toggle switch to go back and forth to where the load would be. It was on an engineer's house and he wanted to switch the thermostat back and forth depending on the season. The other time, I bought 2 wireless thermostats with one receiving station. Whichever thermostat was adjusted last had control of the system. So as long as you don't change the upstairs then the downstairs 10 minutes later, you were fine. It still had the 5 minute waiting period, so you couldn't short cycle it. Its application was the guy had an office he used during the day and wanted it set for his comfort and he rented an apt. out beside him on the same system and when the guy that lived there got home at night, he wanted control and neither one of them wanted the other guy going into their space to control temp while the other one wasn't there. Or you could just buy a zone board and don't put any dampers on it.

  16. #16
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by bmathews View Post
    I've done this before twice. Each of them differently. One time was on a 4 zone Honeywell zone board with 8 thermostats hooked up to it. I simply used a toggle switch to go back and forth to where the load would be. It was on an engineer's house and he wanted to switch the thermostat back and forth depending on the season. The other time, I bought 2 wireless thermostats with one receiving station. Whichever thermostat was adjusted last had control of the system. So as long as you don't change the upstairs then the downstairs 10 minutes later, you were fine. It still had the 5 minute waiting period, so you couldn't short cycle it. Its application was the guy had an office he used during the day and wanted it set for his comfort and he rented an apt. out beside him on the same system and when the guy that lived there got home at night, he wanted control and neither one of them wanted the other guy going into their space to control temp while the other one wasn't there. Or you could just buy a zone board and don't put any dampers on it.

    how many poles did your toggle switch have on it?



    .

  17. #17
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    4,744
    Post Likes
    I believe it was a 3 way toggle switch from Radio Shack. It was about 5 years ago, it gives me a headache to think about it and what a pain in the arse it was to do. Everytime I go to the guys house for service and I see this beast, it makes me shudder and I hope it never breaks, it will take me an hour of staring at it to remember how everything works.

  18. #18
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by bmathews View Post
    it will take me an hour of staring at it to remember how everything works.

    ya i been there and done that!

    imagine what another tech will think when he sees that



    .

  19. #19
    Join Date
    Sep 2006
    Posts
    136
    Post Likes
    Thread Starter
    Quote Originally Posted by bmathews View Post
    Or you could just buy a zone board and don't put any dampers on it.
    And that is another problem with my system. My setup has 4 heat / 2 cool and I'm only aware of one zone board that can be used and it doesn't work with dual fuel. And I read on another thread that zoning the Trane XL16i is not recommended and I'm fairly sure that the AS Heritage 16 is the same as the Trane XL16i. Is that correct?
    Thanks,

    Mark

  20. #20
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    4,744
    Post Likes
    We do a fair amount of strange and off the wall sort of stuff. Lots of high end customers with somewhat odd needs. It's my job to figure out how to make it all work. We've gotten a few calls from customers who have called another company out for service and it confused the hell out of the other tech. Pretty much guaranteed us a customer for life as well as referrals. It makes the job more interesting.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •