  1. #1
    Join Date
    May 2007
    Posts
    80

    What's a CV box?

    Is this different from a VAV box/zone damper?

  2. #2
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,652
    Not really. It's just a box maintaining a fixed CFM setpoint. Still has a damper that modulates.

  3. #3
    Join Date
    Aug 2007
    Location
    WI
    Posts
    1,105
    I think it's a part on a front wheel drive car. Oh, okay, VAV= variable air volume and CV= constant volume. A constant volume box usually just has a hot water and/or chilled water coil in it with no damper in it. Not always the case though.

    On edit: I see orion beat me to it. Damper, no damper, doesn't really matter if it maintains a constant flow.
    Last edited by DesMech; 08-09-2008 at 04:04 PM.

  4. #4
    Join Date
    Dec 2005
    Posts
    107
    it is a VAV box with max and min set the same.
    The important part is that it has a flow sensor to maintain a "pressure independent" constant volume. Otherwise its a balancing damper.

  5. #5
    Join Date
    May 2008
    Location
    Jax Fl.
    Posts
    1,943
    Most of the time CV boxes can maintain temperature without changing the airflow to the space. This is important in areas that need special pressure gradients like operating rooms, radiological pharmacies or chemical labs.

  6. #6
    Join Date
    Apr 2007
    Location
    Amarillo by mornin'
    Posts
    853
    Ya'll have explained what it is but you haven't explained WHAT it is!
    What you are asking to be explained is a fan powered box that runs all of the time. Instead of the fan coming on with just the heat the fan runs all of the time. The fan is actually at the dischage of the box. That means that any air entering the box, either from the plenum or from the inlet damper, it all is being pulled through the fan. Most people call it a mixing box.

    When the box is at set point the inlet damper is either closed or at minimum. So your discharge air that the fan is blowing out is basically plenum air. It's just recurculating. As you need more conditioned air the damper opens more and less plenum air is being pulled in because you are now starting to blow in conditioned air. At 100% cooling the conditioned air that is being blown into the box should be that same amount of air that you are blowing out of the fan. This is where air balance comes into play.

    At 100% the box should be neutral, meaning there is no plenum are being pulled in. Its all conditioned air.

    Hopefully that helps...
    "It's not that I'm smart, it's that I stay with the problem longer”
    Albert Einstein

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event